EMC and inverters
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
marke
post Apr 20 2005, 09:39 AM
Post #1


Posting Freak
******

Group: Moderator
Posts: 2,097
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Inverter (VSDs) are great sources of noise and can cause all sorts of problems.
These problems can be reduced by the correct installation practices. I have a few suggestions and perhaps others can add to the list.


  • Use a screened cable between the motor and the drive. Connect the screen to the motor using a screened gland and connect the screen to the drive using a screened gland.
  • If the screened cable has an earth core, connect it to the earth terminal in the motor and in the drive.
  • Connect all input/output control cables via screened cable terminated at the drive and the control end by screened glands.
  • If the drive does not include an input filter, mount the correct filter as close to the input to the drive as possible. Bond the earth of the filter to the chassis of the drive as close as posible.


      Add your rules also.
      Best regards,


--------------------
Go to the top of the page
 
+Quote Post
Guest__*
post Jul 14 2005, 06:15 PM
Post #2





Guests






mount the drive as close as possible to the motor have the cable lenght in the supply cable and not the motor cable.

Should screen only one end of signal cables to prevent earth loops.
Go to the top of the page
 
+Quote Post
jraef
post Jul 15 2005, 04:04 PM
Post #3


Posting Freak
******

Group: Moderator
Posts: 654
Joined: 22-February 03
From: USA, California
Member No.: 285



And for our North American readers, "screened" means shielded. As of yet, this type of cable is not readily available in the US (although more available in Canada), but if you can find it, that is the best way to go. Look for "tech cable", which is actually a brand name but is being used now generically to describe 3 conductor shielded armored cable.

Anonymous, if you read Marke's post carefully, he meant terminate the earth core conductor at both ends. He had addressed the screen/shield connection by stating that it should be connected at the VFD, which implies only one end, but now that you restated it, that was good clarification.


--------------------
"He's not dead, he's just pinin' for the fjords!"
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   2 honeywell 1,151 20th October 2003 - 07:46 PM
Last post by: grobert
No new   15 easyser 1,258 3rd May 2006 - 03:21 PM
Last post by: jOmega
No New Posts   2 easyser 475 7th July 2006 - 08:09 PM
Last post by: jraef
No New Posts   1 jOmega 541 14th October 2006 - 02:26 AM
Last post by: Rzn
No New Posts   0 rss_aggregator 124 6th May 2008 - 08:40 AM
Last post by: rss_aggregator



RSS Lo-Fi Version Time is now: 21st November 2008 - 02:45 AM
hosted by : L M Photonics Ltd