GUYS, WHY IS IT THAT A CAPACITOR BANK INSTALLATION , IS NOT RECOMMENDED TO THE FOLLOWING:
1.] OPEN TRANSITON MOTOR CONTROL MODES, 2.] DUAL SPEED MOTOR CONFIGURATION, 3.] ELEVATOR MOTOR APPLICATIONS. THANKS IN ADVANCE!! |
|
|
|
Jul 18 2005, 07:54 PM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,099 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hi
Open transition switching does create all sort of potential problems on the supply. The addition of pwer factor correction can exagerate those problems. I have not seen a recommendation as you describe, perhpaps you can give us more detail and we can comment in context. Register on the forum and get notified on replies! Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Jul 22 2005, 08:09 PM
Post
#3
|
|
![]() Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 654 Joined: 22-February 03 From: USA, California Member No.: 285 |
Marke,
In the Eng-Tips forum, I have been involved in a similar thread (thread237-129693) that deals with the same issue. One of our fellow posters has asked a pertinent question as to whether having open transition starters anywhere on the same circuit as the PFC caps would pose a problem. Your thoughts? -------------------- "He's not dead, he's just pinin' for the fjords!"
|
|
|
|
Jul 23 2005, 07:38 AM
Post
#4
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,099 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
I have seen power factor controlled by the starter, i.e. static correction, in many open transition star delta starters without any obvious problems, however after thinking about it, I would suggest that the connection of the power factor correction connected close to the starter during the switching transition, would provide a very low transient supply impedance and could effectively increase the magnitude of the current and torque transients.
If static correction was applied to an open tranistion starter, it would be very easy to effectively over correct the motor in star connection or in low speed connection and this could result in resonance during the open transition stage. This would happen if the correction was permanently connected to the output of the delta contactor. I would suggest that the best way to control the capacitors is with a separate contactor that closes after the transient occurs. The ideal application of static correction will use a separate contactor and detuning reactors. This is not commonly done, but gives much higher protection against the effects of over correction and harmonic currents. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
14 | GGOSS | 2,633 | 2nd January 2008 - 07:14 AM Last post by: jraef |
|||
![]() |
2 | GGOSS | 2,872 | 28th July 2003 - 05:46 AM Last post by: GGOSS |
|||
![]() |
3 | rup_loc | 1,288 | 30th May 2005 - 07:32 PM Last post by: Carl |
|||
![]() |
17 | BigMax | 2,085 | 14th October 2002 - 08:04 AM Last post by: theDOG |
|||
![]() |
8 | -ed- | 1,325 | 15th March 2005 - 12:29 PM Last post by: -Anonymous- |
|||
|
Lo-Fi Version | Time is now: 21st November 2008 - 07:24 PM |