OPEN TRANSITION CONTROL
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
Guest__*
post Jul 18 2005, 05:53 PM
Post #1





Guests






GUYS, WHY IS IT THAT A CAPACITOR BANK INSTALLATION , IS NOT RECOMMENDED TO THE FOLLOWING:

1.] OPEN TRANSITON MOTOR CONTROL MODES,

2.] DUAL SPEED MOTOR CONFIGURATION,

3.] ELEVATOR MOTOR APPLICATIONS.


THANKS IN ADVANCE!!
Go to the top of the page
 
+Quote Post
marke
post Jul 18 2005, 07:54 PM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,099
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hi

Open transition switching does create all sort of potential problems on the supply. The addition of pwer factor correction can exagerate those problems.

I have not seen a recommendation as you describe, perhpaps you can give us more detail and we can comment in context.

Register on the forum and get notified on replies!
Best regards,


--------------------
Go to the top of the page
 
+Quote Post
jraef
post Jul 22 2005, 08:09 PM
Post #3


Posting Freak
******

Group: Moderator
Posts: 654
Joined: 22-February 03
From: USA, California
Member No.: 285



Marke,
In the Eng-Tips forum, I have been involved in a similar thread (thread237-129693) that deals with the same issue. One of our fellow posters has asked a pertinent question as to whether having open transition starters anywhere on the same circuit as the PFC caps would pose a problem.

Your thoughts?


--------------------
"He's not dead, he's just pinin' for the fjords!"
Go to the top of the page
 
+Quote Post
marke
post Jul 23 2005, 07:38 AM
Post #4


Posting Freak
******

Group: Moderator
Posts: 2,099
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



I have seen power factor controlled by the starter, i.e. static correction, in many open transition star delta starters without any obvious problems, however after thinking about it, I would suggest that the connection of the power factor correction connected close to the starter during the switching transition, would provide a very low transient supply impedance and could effectively increase the magnitude of the current and torque transients.
If static correction was applied to an open tranistion starter, it would be very easy to effectively over correct the motor in star connection or in low speed connection and this could result in resonance during the open transition stage. This would happen if the correction was permanently connected to the output of the delta contactor.
I would suggest that the best way to control the capacitors is with a separate contactor that closes after the transient occurs.

The ideal application of static correction will use a separate contactor and detuning reactors. This is not commonly done, but gives much higher protection against the effects of over correction and harmonic currents.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No new   14 GGOSS 2,633 2nd January 2008 - 07:14 AM
Last post by: jraef
No New Posts   2 GGOSS 2,872 28th July 2003 - 05:46 AM
Last post by: GGOSS
No New Posts   3 rup_loc 1,288 30th May 2005 - 07:32 PM
Last post by: Carl
No new   17 BigMax 2,085 14th October 2002 - 08:04 AM
Last post by: theDOG
No New Posts   8 -ed- 1,325 15th March 2005 - 12:29 PM
Last post by: -Anonymous-



RSS Lo-Fi Version Time is now: 21st November 2008 - 07:24 PM
hosted by : L M Photonics Ltd