3ph compressor motor tripping |
![]() ![]() |
3ph compressor motor tripping |
Jul 30 2005, 10:34 AM
Post
#1
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 2 Joined: 30-July 05 Member No.: 1,168 |
I have just installed a second hand 3ph 7.5kw compressor, and it keeps tripping the breaker in its box on start up.
there are 3 contactors in its box, 2 of which pull in and the motor stars to turn. the motor will then trip, sometimes before the other contactor pulls in, sometimes after. There is a timer (0-30 secs) in the box with an led which sometimes flashes if it pulls the 3rd contactor in. The compressor ran ok at another site, all i have done is connect 2 phases and a neutral to the existing wires. Both phases are 240v. Any ideas ? |
|
|
|
Jul 30 2005, 12:33 PM
Post
#2
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 2 Joined: 30-July 05 Member No.: 1,168 |
newbie question relating to topic below.
Do I need to connect all 3 phases to my motor/starter or just 2 ? I currently have 2 ans the other red wire from motor/starter to neutral. There are 3 red wires and an earth coming from the compressor. |
|
|
|
Jul 30 2005, 10:31 PM
Post
#3
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,060 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello autopaint
Welcome to the forum It sounds to me as though you are trying to run a three pahse motor on two phases. The starter that you are using is a star/delta starter. You must connect a three phase motor to three phases. If you only use two phases, you will damage the motor and it will not start correctly. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Jul 31 2005, 11:24 PM
Post
#4
|
|
|
Senior Member ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 404 Joined: 17-May 02 From: Melbourne Member No.: 14 |
Hello autopaint,
Certainly sounds like you have a star/delta starter installed. That being the case (as indicated by Marke) they need a 3-phase supply to operate correctly. The fact that you are connecting 2 phases and a neutral is more than likely the cause of your CB trip conditions. Regards, GGOSS |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
2 | GGOSS | 2,491 | 28th July 2003 - 05:46 AM Last post by: GGOSS |
|||
![]() |
0 | marke | 2,599 | 11th June 2002 - 10:32 PM Last post by: marke |
|||
![]() |
0 | marke | 2,062 | 11th June 2002 - 10:34 PM Last post by: marke |
|||
![]() |
0 | marke | 1,803 | 11th June 2002 - 10:42 PM Last post by: marke |
|||
![]() |
0 | marke | 1,875 | 12th June 2002 - 09:24 AM Last post by: marke |
|||
|
Lo-Fi Version | Time is now: 28th August 2008 - 05:14 PM |