Why is that all electrical panels come with control voltage transformers.
Say a panel has 380 V 3 phase incomer...then 2 phases are taken into a 380v to 220 v transformer, and this voltage is used in control circuits. What is the advantage of this system? Can we put a 13.8 kv/ 220/110 volts dyn11 transformer and use 220 volts supply ( phase to phase ) for control voltage in 33/13.8kv substations? chaterpilar |
|
|
|
Dec 2 2005, 12:04 PM
Post
#2
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Members Posts: 16 Joined: 10-November 05 Member No.: 1,276 |
Control transformers are provided mainly for following reasons
1. To have isolation from the Main supply 2. To limit fault levels in control ciruit 3. To have a safer and lower control voltage As far as second part of the question is concerned if u are planning to take secondary of the MAin transformer it msy not be a good idea ( Sl No 2 above ) It is also a good practice to use secondary centre tap earthed control transformers so that those working on the system are subjected to a lesser voltage w.r.t ground |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
14 | GGOSS | 2,633 | 2nd January 2008 - 07:14 AM Last post by: jraef |
|||
![]() |
2 | GGOSS | 2,872 | 28th July 2003 - 05:46 AM Last post by: GGOSS |
|||
![]() |
3 | rup_loc | 1,288 | 30th May 2005 - 07:32 PM Last post by: Carl |
|||
![]() |
17 | BigMax | 2,087 | 14th October 2002 - 08:04 AM Last post by: theDOG |
|||
![]() |
8 | -ed- | 1,325 | 15th March 2005 - 12:29 PM Last post by: -Anonymous- |
|||
|
Lo-Fi Version | Time is now: 21st November 2008 - 09:09 PM |