Hello and welcome to LMPForum, like most online communities you must register to view or post in our community, but don't worry this is a simple free process that requires minimal information. Take advantage of it immediately Register Now There are many great features that are not available to guests at LMPForum |
Forgot Password |
![]() ![]() |
2 % Diff In Voltage - 40 % Diiff In Current |
Aug 1 2009, 08:06 PM
Post
#1
|
|
|
Member ![]() ![]() ![]() ![]() Group: Full Member Posts: 78 Joined: 13-June 09 Member No.: 5,502 |
I have (seen) a 3 ph induction 380 V motor running with current difference of about 40 % caused by voltage difference of about 2 % across phases. This because taps on the supply transformer were set wrongly. I doubt the phenomena could be explained but does anyone else has encountered a similar case - insignificant diff in V supply leading to huge diff in A drawn ? The amps (if I remember good) were some 90/120/140 A.
|
|
|
|
Aug 1 2009, 09:21 PM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,336 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello Yuri
This is not uncommon and occurs primarily at light load. If you consider the induction motor as being a resistive load and a generator, then you can see how this can happen. The motor is driven by the supply with a rotating magnetic field in the stator resulting form the applied voltage. The rotating magnetic field in the stator causes a magnetic field in the rotor which is spinning at the same speed as the stator field. The rotor field causes a voltage to be generated in the stator in the same manner as a DC motor and this subtracts from the supply voltage. The generated voltage is not balanced in voltage and phase and subtracting this from the unbalanced supply voltage can exaggerate the difference or reduce the difference. Rotating the connections to the motor will alter the current balance with a particular connection minimising the imbalance. The basic imbalance in the motor is due to the imbalance in the iron inductance and is primarily due to the grain orientation of the steel used for the stator laminations. As the resistive component of current increases, the measured current imbalance will reduce, so the imbalance reduces with load. Best regards, Mark. -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Aug 2 2009, 06:56 AM
Post
#3
|
|
|
Member ![]() ![]() ![]() ![]() Group: Full Member Posts: 78 Joined: 13-June 09 Member No.: 5,502 |
Hello Mark
I have "rotated" the leads to the motor as my first idea was unbelief that such small inbalance in V could cause such huge curr inbalance and I suspected the motor. But the inbalance just transferred - precisely the same readings now on the other leads. Other motors (less powerfull) fed from that transformer have a less conspicuous difference in currents between phases. Best regards Yuri |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
1 | -shahbaz ali- | 4,098 | 28th August 2002 - 09:32 AM Last post by: marke |
|||
![]() |
0 | -shahbaz ali- | 1,943 | -- Last post by: shahbaz ali |
|||
![]() |
10 | theDOG | 2,550 | 25th September 2002 - 10:39 AM Last post by: marke |
|||
![]() |
5 | magdy El Kady | 2,008 | 26th September 2002 - 10:10 AM Last post by: GGOSS |
|||
![]() |
1 | tom | 4,584 | 15th August 2003 - 04:00 PM Last post by: merajdab |
|||
|
Lo-Fi Version | Time is now: 15th March 2010 - 06:07 AM |