3ph compressor motor tripping
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
autopaint
post Jul 30 2005, 10:34 AM
Post #1


Junior Member
**

Group: Members
Posts: 2
Joined: 30-July 05
Member No.: 1,168



I have just installed a second hand 3ph 7.5kw compressor, and it keeps tripping the breaker in its box on start up.
there are 3 contactors in its box, 2 of which pull in and the motor stars to turn. the motor will then trip, sometimes before the other contactor pulls in, sometimes after.
There is a timer (0-30 secs) in the box with an led which sometimes flashes if it pulls the 3rd contactor in.
The compressor ran ok at another site, all i have done is connect 2 phases and a neutral to the existing wires. Both phases are 240v.

Any ideas ?
Go to the top of the page
 
+Quote Post
autopaint
post Jul 30 2005, 12:33 PM
Post #2


Junior Member
**

Group: Members
Posts: 2
Joined: 30-July 05
Member No.: 1,168



newbie question relating to topic below.
Do I need to connect all 3 phases to my motor/starter or just 2 ? I currently have 2 ans the other red wire from motor/starter to neutral. There are 3 red wires and an earth coming from the compressor.
Go to the top of the page
 
+Quote Post
marke
post Jul 30 2005, 10:31 PM
Post #3


Posting Freak
******

Group: Moderator
Posts: 2,099
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello autopaint

Welcome to the forum

It sounds to me as though you are trying to run a three pahse motor on two phases. The starter that you are using is a star/delta starter.
You must connect a three phase motor to three phases. If you only use two phases, you will damage the motor and it will not start correctly.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post
GGOSS
post Jul 31 2005, 11:24 PM
Post #4


Senior Member
*****

Group: Moderator
Posts: 404
Joined: 17-May 02
From: Melbourne
Member No.: 14



Hello autopaint,

Certainly sounds like you have a star/delta starter installed. That being the case (as indicated by Marke) they need a 3-phase supply to operate correctly. The fact that you are connecting 2 phases and a neutral is more than likely the cause of your CB trip conditions.

Regards,
GGOSS
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   2 GGOSS 2,872 28th July 2003 - 05:46 AM
Last post by: GGOSS
No New Posts   0 marke 3,282 11th June 2002 - 10:32 PM
Last post by: marke
No New Posts   0 marke 2,578 11th June 2002 - 10:34 PM
Last post by: marke
No New Posts   0 marke 2,191 11th June 2002 - 10:42 PM
Last post by: marke
No New Posts   0 marke 2,041 12th June 2002 - 09:24 AM
Last post by: marke



RSS Lo-Fi Version Time is now: 21st November 2008 - 06:54 PM
hosted by : L M Photonics Ltd