Asymmetry Fault 11kv Motor, CET4 protection pick up
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
ljessop
post Dec 26 2008, 03:17 AM
Post #1


Junior Member
**

Group: Members
Posts: 2
Joined: 26-December 08
Member No.: 5,047



Good morning/ evening all.
I have just recieved a call in regards to an asymmetry fault on an 11kV motor.
We have low resistance tested the rotor {wound rotor with liquid resistance starter with power factor correction banks}. Checked all brush connections, inspected the 11kV circuit breaker and even tested the relay for the starter. The only thing that has not been done, is the star point on the HV motor lifted and tested the individual windings. My suspicion is that we have a shorted turn/s in the windings. We do not have the gear to turns/ratio test the windings available, but we have a spare motor. The power factor bank has been checked as well and is okay.

Background: Suspected direct lightening strike during storm.....

The assymetry fault has not been seen before, but I would suspect that the current is pulling back the voltage in one phase giving an imbalance.

Need some input.............rapidly !


Go to the top of the page
 
+Quote Post
marke
post Dec 26 2008, 07:49 PM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,336
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello ljessop

Welcome to the forum.

If you suspect that you may have sorted turns in the stator, then one thing that you can easily do, is to put a low voltage across each winding in turn and measure the current draw. The motor will not try to rotate.
I would suggest that if the motor is star connected, you try around 230VAC from the star point to each phase input and you should get a measurable current flow. If the currents are all even, then the windings are probably OK or are breaking down under voltage. If you have an imbalance in current, then you have a winding issue. (I typically use 24VAC for a 400V motor)

Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post
ljessop
post Dec 27 2008, 01:14 AM
Post #3


Junior Member
**

Group: Members
Posts: 2
Joined: 26-December 08
Member No.: 5,047



QUOTE (marke @ Dec 26 2008, 07:49 PM) *
Hello ljessop

Welcome to the forum.

If you suspect that you may have sorted turns in the stator, then one thing that you can easily do, is to put a low voltage across each winding in turn and measure the current draw. The motor will not try to rotate.
I would suggest that if the motor is star connected, you try around 230VAC from the star point to each phase input and you should get a measurable current flow. If the currents are all even, then the windings are probably OK or are breaking down under voltage. If you have an imbalance in current, then you have a winding issue. (I typically use 24VAC for a 400V motor)

Best regards,
Mark.



Thanks mark. We split the star point and resistance tested the windings. No real problems. Went back to the LRS and found a high resistance across the contactor on one phase that feeds the slip rings.
Cheers,

Luke


Go to the top of the page
 
+Quote Post
marke
post Dec 27 2008, 04:04 AM
Post #4


Posting Freak
******

Group: Moderator
Posts: 2,336
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hi Luke

Thanks for the feedback. So often we are left in a vacuum as to whether the advise has helped or not.

Sounds like you got it sorted.
Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   2 GGOSS 4,666 28th July 2003 - 05:46 AM
Last post by: GGOSS
No New Posts   2 marke 6,829 4th July 2009 - 05:27 AM
Last post by: marke
No New Posts   0 marke 5,318 11th June 2002 - 10:34 PM
Last post by: marke
No New Posts   1 marke 3,828 7th December 2009 - 10:32 AM
Last post by: Broshi
No New Posts   0 marke 2,770 12th June 2002 - 09:24 AM
Last post by: marke


RSS Lo-Fi Version Time is now: 14th March 2010 - 03:31 PM

Tag cloud:

hosted by : L M Photonics Ltd
LMPhotonics Home  Power factor  Motor Control  Single Phase Motors  Slipring Motors  Motor Starters  Soft Starters  Variable Speed  Energy Savers