Hello and welcome to LMPForum, like most online communities you must register to view or post in our community, but don't worry this is a simple free process that requires minimal information. Take advantage of it immediately Register Now There are many great features that are not available to guests at LMPForum |
Forgot Password |
![]() ![]() |
Atv71 Protection Settings, thermal protection |
Sep 17 2009, 07:33 AM
Post
#1
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 4 Joined: 14-September 09 Member No.: 6,526 |
could someone please explain why the motor thermal protection setting on a ATV71 is set to 118%
where does this figure come from? if this is an allowance for service factor of the motor which i understood to be 115% am i right in assuming that anything above 100% contributes to a shorter motor life? is this the equivilent of other manufactures 100% setting (eg GE369 MM2 etc) who quote 100% thermal should be the trip? |
|
|
|
Sep 17 2009, 10:19 AM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,383 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
QUOTE motor thermal protection setting on a ATV71 is set to 118% Where does this figure / recommendation come from? Best regards, Mark. -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Sep 18 2009, 04:44 AM
Post
#3
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 4 Joined: 14-September 09 Member No.: 6,526 |
Where does this figure / recommendation come from? Best regards, Mark. from the ATV71 programming manual "tHt- b [MOTOR THERMAL PROT.] Note: A fault trip will occur when the thermal state reaches 118% of the rated state and reactivation will occur when the state falls back below 100%." this isnt an obscure parameter, this is the main motor protection. It appears that the ATV71 motor thermal protection is set by default (and cannot be changed) to 118% of the motor thermal state which is calculated by the drive using frequency, time, current, cooling method and an ambient of 40 degrees this i am told by schnieder complies with IEC947-4 however this doesnt answer my question to them Q Although the motor may be protected from short term burnout, would running a motor above 100% but below the trip point (118%) decrease the motors life. i realise this could be achieved by reducing the Motor Thermal setting ITH to 85% of the motor nominal current as opposed to the programming manual which states "Motor thermal protection current, to be set to the rated current indicated on the nameplate". i would still like to understand the reasoning behind th 118% and how it compares with other motor protection relays which state 100% |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
0 | marke | 6,095 | 11th June 2002 - 10:34 PM Last post by: marke |
|||
![]() |
1 | -mahesh- | 2,314 | 4th April 2006 - 06:08 AM Last post by: khongai |
|||
![]() |
3 | tahira | 4,048 | 22nd August 2003 - 09:01 AM Last post by: sethar |
|||
![]() |
0 | tahira | 1,072 | -- Last post by: tahira |
|||
![]() |
1 | normannicklette | 2,721 | 1st November 2004 - 08:01 AM Last post by: RalphChristie |
|||
|
Lo-Fi Version | Time is now: 3rd September 2010 - 05:12 PM |