Auto Transformer Star Point
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
Jakes
post Dec 25 2008, 07:23 PM
Post #1



*

Group: Members
Posts: 1
Joined: 25-December 08
Member No.: 5,045



I am in the Electrical training field and motors are run at no load. I have noticed that whether the three phase auto transformer star is open or closed makes no difference. Can somebody please give me the reason why the star point must be closed during start up?


Go to the top of the page
 
+Quote Post
marke
post Dec 25 2008, 07:59 PM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,336
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Jakes

Welcome to the forum

When the star point is closed, the transformer supplies a reduced voltage to the motor where the voltage is determined by the transformer ratio.
When the star point is open, the transformer behaves as a primary reactor and the voltage applied to the motor is determined by the ratio of the motor impedance to the total impedance of the motor plus the reactance of the transformer.

There will be a difference in start current between the star point closed and the star point open with lower start current in the line for the star point closed.

Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post
Marco
post Apr 28 2009, 09:04 AM
Post #3


Junior Member
**

Group: Members
Posts: 3
Joined: 28-April 09
From: Perth
Member No.: 5,336



As a follow-up to this question, I assume that for a standard 50/65/80% autotransformer, only 64% of the motor full load current rating will suffice for the current rating of the transformer contactor, as this covers the "worst-case scenario" of the 80% tap being selected for use (please correct me if I am wrong there).

What I would like to know though is what rating is recommended for the star contactor?
The current through it will be negligible, right?


Go to the top of the page
 
+Quote Post
marke
post Apr 28 2009, 10:09 AM
Post #4


Posting Freak
******

Group: Moderator
Posts: 2,336
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Marco

The current flowing to the motor is directly proportional to the voltage reduction.
The current flowing in the supply is proportional to the square of the voltage reduction. Therefore the curent from the 80% tap is 80%, not 64%.

Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post
Marco
post Apr 28 2009, 11:57 PM
Post #5


Junior Member
**

Group: Members
Posts: 3
Joined: 28-April 09
From: Perth
Member No.: 5,336



QUOTE (marke @ Apr 28 2009, 06:09 PM) *
The current flowing to the motor is directly proportional to the voltage reduction.
The current flowing in the supply is proportional to the square of the voltage reduction. Therefore the curent from the 80% tap is 80%, not 64%.

Mark,
Yes, but the transformer contactor is installed on the primary side of the transformer, so it would see only 64% current flowing through it, right?


Go to the top of the page
 
+Quote Post
marke
post Apr 29 2009, 07:04 PM
Post #6


Posting Freak
******

Group: Moderator
Posts: 2,336
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Marco

Yes, that is correct provided that you are using a single stage Korndorffer auto transformer starter and that the contactor is bypassed when full voltage is applied.
In some installations, that contactor is used as a main contactor and remains in circuit while the motor is running. This makes it easy to fit the overloads etc, otherwise you do not have a common path for the overloads to be connected and so they are out of circuit during start.

Best regards,


--------------------


Go to the top of the page
 
+Quote Post
Marco
post Apr 30 2009, 12:57 AM
Post #7


Junior Member
**

Group: Members
Posts: 3
Joined: 28-April 09
From: Perth
Member No.: 5,336



Yes, fair enough.

Back to my original query then ... is there a standard "rule of thumb" used for sizing the star contactor?
For commonality of equipment I would probably just use the same rating as the transformer contactor, but I am also thinking that you could potentially make it a lot smaller to save on space & cost.
It is really just a voltage reference point, with negligible current flowing through it - is that correct?


Go to the top of the page
 
+Quote Post
marke
post Apr 30 2009, 06:46 PM
Post #8


Posting Freak
******

Group: Moderator
Posts: 2,336
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Marco

The star contactor carries the motor current plus the transformer current so would need to be at least the size of the motor current.

Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   11 Alnerthyrn 3,297 29th March 2005 - 02:44 AM
Last post by: jraef
No New Posts   3 tahira 5,571 21st May 2004 - 06:28 AM
Last post by: -Anonymous-
No new   32 kongkc 7,042 13th November 2005 - 07:09 PM
Last post by: -Anonymous-
No New Posts   1 Roomsk10 1,808 19th March 2003 - 09:59 AM
Last post by: marke
No New Posts   5 noble 3,319 9th June 2003 - 11:16 AM
Last post by: marke


RSS Lo-Fi Version Time is now: 13th March 2010 - 09:36 PM

Tag cloud:

hosted by : L M Photonics Ltd
LMPhotonics Home  Power factor  Motor Control  Single Phase Motors  Slipring Motors  Motor Starters  Soft Starters  Variable Speed  Energy Savers