hi . m about to install 2 by 10kw motors using star delta starter. flc of each motor is 25A. what should be the size of the cable.
Go to the top of the page
 
+Quote Post
chrisevo
post Mar 4 2008, 02:11 PM
Post #2


Junior Member
**

Group: Full Member
Posts: 6
Joined: 7-February 08
From: England
Member No.: 4,267



I would need to know how long cables are to be and of what type?
Go to the top of the page
 
+Quote Post
Jay Tee
post Mar 5 2008, 03:18 AM
Post #3


Junior Member
**

Group: Members
Posts: 3
Joined: 25-February 08
Member No.: 4,325



QUOTE (illusions @ Mar 4 2008, 05:49 PM) *
hi . m about to install 2 by 10kw motors using star delta starter. flc of each motor is 25A. what should be the size of the cable.

There are a lot of ways to determine the cable size since different type of cable may have different ampere rating. However, for minimum requirement, you may use the following formula:

For DC and single phase motor
S= (2.L.I. pf)/(C.VU) or
S = (2.L.P)/(C.VU.U)

For Three Phase motor:
S=(1.73.L.I.pf)/(C.VU) or
S = (L.P)/(C.VU.U)

where
S = cable size in mm sq
L = cable length in meter
I = Rated ampere
P = power of motor in watt
CU = Voltage drop allowable( such as 2.5% of usage voltage)..depend on country regulation
U = Voltage
pf = power factor
C = conductivity of cable if Cu = 56, Al = 35, Fe = 8.5

To get the final result, S shall be divided with the temperature surrounding factor:

20 Deg C: 1.4
25 Deg C : 1.3
30 Deg C : 1.22
35 Deg C : 1.13
40 Deg. C : 1.00
45 Deg. C : 0.87

For example, S = 3.5 with surrounding temperature around 45 Deg. C, then the final result shall be

(3.5)/(0.87). From here, you will select the cable size based on the standard manufacturer available like 1.5, 2.5, 4.0 and etc. For safety, I would suggest you choose one step higher then the final result.


Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   6 potdar 1,454 21st September 2003 - 11:11 PM
Last post by: electricpete
No New Posts   0 amrh 1,251 4th December 2002 - 12:32 PM
Last post by: amrh
No New Posts   1 -necr- 1,688 17th January 2003 - 07:44 PM
Last post by: marke
No New Posts   1 -Anonymous- 1,379 15th January 2004 - 07:11 PM
Last post by: marke
No New Posts   2 -Anonymous- 792 8th January 2005 - 12:24 AM
Last post by: jraef



RSS Lo-Fi Version Time is now: 21st November 2008 - 03:55 PM
hosted by : L M Photonics Ltd