Calculate Kw Rating Of Motor, Chillers Kw Rating
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
normanundercroft
post Apr 21 2009, 03:16 PM
Post #1


Junior Member
**

Group: Members
Posts: 2
Joined: 21-April 09
Member No.: 5,327



We have two chillers at work to cool the offices.
We know the start current and running current and they are star delta start.
How do we calculate the KW rating of the motor so we can size a gen set to keep them running during a power cut? mellow.gif


Go to the top of the page
 
+Quote Post
marke
post Apr 23 2009, 10:00 AM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,336
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello normanundercroft

Welcome to the forum.

It is not really practical to calculate the KW rating of a motor from it's running current and start current.
To size your generator, there are two major considerations in terms of the load side.
The alternator is loaded by KVA (Amps) and the engine is loaded by KW.

To size your generator, measure the continuous KW drawn by the motors, and the peak KW drawn during start. This will determine the continuous rating of the engine and the peak rating of the engine.
You need to make an allowance for the KW losses in the alternator and cables during start.
Some engines have a good overload margin such as 300% for 10 seconds, while others will only allow 120% for 10 seconds.

Measure the starting current and the run current of the motors and calculate the KVA (V x I x rt3 / 1000). This will determine the continuous rating and the overload rating of the alternator.
If the alternator is fitted with permanent magnet excitation and a three phase averaging AVR, it is possible that the alternator may be able to withstand 300% for 10 seconds or even more. The more common single phase peak AVR and self excitation will probably only allow an overload of 20% (120% load) for 10 seconds or less.

The problem with the star delta starter for this application, is that there is a high current transient as the starter switches from star to delta. This can cause problems with heavily loaded generator sets.
I would suggest that a soft starter may be a better option.

Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   2 GGOSS 4,658 28th July 2003 - 05:46 AM
Last post by: GGOSS
No New Posts   2 marke 6,810 4th July 2009 - 05:27 AM
Last post by: marke
No New Posts   0 marke 5,291 11th June 2002 - 10:34 PM
Last post by: marke
No New Posts   1 marke 3,812 7th December 2009 - 10:32 AM
Last post by: Broshi
No New Posts   0 marke 2,769 12th June 2002 - 09:24 AM
Last post by: marke


RSS Lo-Fi Version Time is now: 11th March 2010 - 11:15 PM

Tag cloud:

hosted by : L M Photonics Ltd
LMPhotonics Home  Power factor  Motor Control  Single Phase Motors  Slipring Motors  Motor Starters  Soft Starters  Variable Speed  Energy Savers