Centrifugal Compressor
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
anu_rags
post Jan 8 2009, 03:23 PM
Post #1


Intermediate Member
***

Group: Full Member
Posts: 35
Joined: 27-June 06
From: India, Vadodara
Member No.: 1,583



Dear All,

I need some urgent help for selecting Softstarter for Centrifugal compressor application. Im attaching the load torque curve of the compressor. http://rapidshare.com/files/181073531/win6...Curve_50_Hz.pdf. Starting time required for the compressor is 5-12 seconds.

Motor details are AMbient temp = 45 deg c
Motor rating = 410 KW
Operating volt = 415 +/- 10%, 3 ph, 50 Hz +/- 3%
Full load current = 650 A

I have selected Emotron Softstarter of 500kw rating, 710A current with 300% overload for 30 sec. Will this be suitable for this compressor? How do we determine from the load torque curve of compressor, that it can be started with a softstarter? Presently he is using FCMA type starter and want to switch to SCR soft starter.

Regards,
Anurag


Go to the top of the page
 
+Quote Post
marke
post Jan 8 2009, 06:04 PM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,336
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Anurag

First, yes you can use a soft starter to start this compressor, but the start current is a function of the speed/torque curve of the compressor and the speed/torque and speed/current curves of the motor.

There are major variations between the start characteristics of motors and the start current variation for a given load can vary by more that 50% depending on the motor.

Do you have any data on the motor? I would need this to comment. Without this data, I would allow for a start current of 400 - 450% from my experience.

Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   3 bbeer 1,525 29th November 2004 - 03:44 AM
Last post by: -Anonymous-
No New Posts   1 bingobong62 1,070 5th November 2003 - 06:41 PM
Last post by: marke
No New Posts   3 autopaint 982 31st July 2005 - 11:24 PM
Last post by: GGOSS
No New Posts   5 RCinFL 4,536 20th September 2005 - 01:18 AM
Last post by: RCinFL
No New Posts   3 sanjoy_datta49 1,447 28th September 2005 - 02:26 PM
Last post by: -Anonymous-


RSS Lo-Fi Version Time is now: 15th March 2010 - 10:36 PM

Tag cloud:

hosted by : L M Photonics Ltd
LMPhotonics Home  Power factor  Motor Control  Single Phase Motors  Slipring Motors  Motor Starters  Soft Starters  Variable Speed  Energy Savers