Hello and welcome to LMPForum, like most online communities you must register to view or post in our community, but don't worry this is a simple free process that requires minimal information. Take advantage of it immediately Register Now There are many great features that are not available to guests at LMPForum |
Forgot Password |
![]() ![]() |
Over Correction, power factor |
Nov 9 2008, 07:37 AM
Post
#1
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Full Member Posts: 14 Joined: 15-August 07 Member No.: 3,633 |
If the capacitor of a plant is over corrected such that plant net power factor become leading, what will be its effect on the electrical system as well as the supply company. kindly give me a suitable answere, thank u. |
|
|
|
Nov 9 2008, 07:53 AM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,336 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Generally, a leading power factor attracts the same penalties as a lagging power factor.
There should be no problems with a leading power factor under most supply connections, but some reactive supplies may be affected by a leading power factor. A lagging power factor causes an increase in supply current. A Leading power factor also increases the supply current. Best regards, Mark. -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Dec 2 2008, 05:00 PM
Post
#3
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 4 Joined: 27-November 08 Member No.: 4,988 |
The electricity supply utilities generally specify a power factor of 0.8 to 0.9.
Compensation beyond cos ϕ = 1 (over-compensation Qc > Q1) must be avoided as this gives rise to capacitive reactive power which stresses the conductors in the same way as inductive reactive power, and in addition, unwelcome voltage increases can occur. For a short discussion you can refer to Electrical riddle No.31 from http://electrical-riddles.com |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
1 | Itos | 2,774 | 26th June 2002 - 08:56 PM Last post by: marke |
|||
![]() |
1 | marke | 2,662 | 2nd November 2006 - 03:23 AM Last post by: AB2005 |
|||
![]() |
1 | Lewis | 1,932 | 28th September 2002 - 01:37 AM Last post by: marke |
|||
![]() |
3 | Lewis | 1,918 | 8th October 2002 - 05:53 PM Last post by: marke |
|||
![]() |
5 | metro | 2,252 | 10th December 2004 - 12:09 PM Last post by: -Anonymous- |
|||
|
Lo-Fi Version | Time is now: 16th March 2010 - 02:24 PM |