Drive Speed Range
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
AB2005
post Nov 25 2009, 05:59 AM
Post #1


Senior Member
*****

Group: Full Member
Posts: 301
Joined: 21-October 06
Member No.: 2,159



Hello Friends;

I have one question and wandering for its answer. In the literature of AC/DC drives, a term “speed range” (say 50:1 open loop and 200:1 when closed loop) describes, can anyone explain about it? I am not known about it.


--------------------
"Don't assume any thing, always check/ask and clear yourself".


Go to the top of the page
 
+Quote Post
AB2005
post Nov 27 2009, 04:46 AM
Post #2


Senior Member
*****

Group: Full Member
Posts: 301
Joined: 21-October 06
Member No.: 2,159



For refrenece, please see the attached image or click the following link;

http://www.joliettech.com/dc_drive_types.htm

Attached File(s)
Attached File  Image.JPG ( 134.06K ) Number of downloads: 5
 


--------------------
"Don't assume any thing, always check/ask and clear yourself".


Go to the top of the page
 
+Quote Post
yuri
post Nov 27 2009, 06:18 PM
Post #3


Member
****

Group: Full Member
Posts: 78
Joined: 13-June 09
Member No.: 5,502



QUOTE (AB2005 @ Nov 27 2009, 05:46 AM) *
For refrenece, please see the attached image or click the following link;

http://www.joliettech.com/dc_drive_types.htm

No conception. Somewhat fuzzy short articles - seems they have confused, by omission, basic and maximal speeds in their explanations of the constant power/torque.
Best regards.


Go to the top of the page
 
+Quote Post
AB2005
post Nov 30 2009, 03:27 AM
Post #4


Senior Member
*****

Group: Full Member
Posts: 301
Joined: 21-October 06
Member No.: 2,159



QUOTE (yuri @ Nov 27 2009, 11:18 PM) *
No conception. Somewhat fuzzy short articles - seems they have confused, by omission, basic and maximal speeds in their explanations of the constant power/torque.
Best regards.


Hello yuri,

I have read about "drive speed range" from two to three places. For example, click on the bellow link where you would see that rockwell automation too quoted drive speed range after tables.

Rockwellautomation

Looking forward for a detailed answer from someone.


--------------------
"Don't assume any thing, always check/ask and clear yourself".


Go to the top of the page
 
+Quote Post
ggalea
post Nov 30 2009, 03:16 PM
Post #5


Junior Member
**

Group: Members
Posts: 4
Joined: 26-November 09
Member No.: 7,194



QUOTE (AB2005 @ Nov 25 2009, 12:59 AM) *
Hello Friends;

I have one question and wandering for its answer. In the literature of AC/DC drives, a term "speed range" (say 50:1 open loop and 200:1 when closed loop) describes, can anyone explain about it? I am not known about it.


Hi Yuri: Here is the definition for speed range:

The minimum and maximum speeds at which a motor must operate under constant or variable torque load conditions.
For example:
A 4:1 speed range for a motor with a top speed of 1800 rpm means that the motor must be able to operate as low as 450 rpm and still remain within regulation specifications. The controllable speed range of a motor is limited by the ability to deliver required torque below base speed without additional cooling.
Hope this helped you, George


Go to the top of the page
 
+Quote Post
AB2005
post Nov 30 2009, 03:57 PM
Post #6


Senior Member
*****

Group: Full Member
Posts: 301
Joined: 21-October 06
Member No.: 2,159



QUOTE (ggalea @ Nov 30 2009, 09:16 PM) *
Hi Yuri: Here is the definition for speed range:

The minimum and maximum speeds at which a motor must operate under constant or variable torque load conditions.
For example:
A 4:1 speed range for a motor with a top speed of 1800 rpm means that the motor must be able to operate as low as 450 rpm and still remain within regulation specifications. The controllable speed range of a motor is limited by the ability to deliver required torque below base speed without additional cooling.


Thanks ggalea;

For example, there has been quoted with a drive 200:1 speed range. If motor is 1800rpm then it means motor can run at 9rpm within regulation spec? Some drives manufacturers quote 1000:1 (see in the link posted in my previous mail), what its means?


Discussion always leads to everyone to the right point.


--------------------
"Don't assume any thing, always check/ask and clear yourself".


Go to the top of the page
 
+Quote Post
ggalea
post Dec 1 2009, 10:51 PM
Post #7


Junior Member
**

Group: Members
Posts: 4
Joined: 26-November 09
Member No.: 7,194



QUOTE (AB2005 @ Nov 30 2009, 10:57 AM) *
Thanks ggalea;

For example, there has been quoted with a drive 200:1 speed range. If motor is 1800rpm then it means motor can run at 9rpm within regulation spec? Some drives manufacturers quote 1000:1 (see in the link posted in my previous mail), what its means?


Discussion always leads to everyone to the right point.


Yuri: These are from my notes:

Mostly, these speed ranges are applicable to Constant torque loads
Applications include: Conveyors, elevators, hoists, extruders, positive displacement pumps, mixers and converting equipment.

Torque remains constant throughout the range of operation, and extra care should be taken in the proper application of motors, especially at very low speeds. Most constant torque (C.T.) applications don't require operation below 10:1 (i.e. 6 Hz operation on a 60 Hz motor), but an increasing number of applications historically reserved for servo and/or stepper systems are being served with motors capable of operation beyond 20:1…even up to 2000:1 (zero speed, constant torque).

Applications requiring greater than 20:1 C.T. are ideal for certain electric that advertise these type of motor specs.
These motors provide full rated torque within their listed speed range, without exceeding a Class F temperature rating while under inverter power (many operate at Nema Design Class B insulation). Ratings have been developed, based on extensive testing on IGBT inverters, set at a minimum 3 KHz (or equivalent) carrier frequency. Carrier frequency is the switching frequency of the IGBTs. The higher you go the hotter the motor gets deep inside the windings. If you are going to take the temperature of the motor with a temp gun, always wait until the motor is powered OFF, wait about 5 minutes, then take the temperature of the motor skin. This allows for the heat to egress to the outside skin of the motor hence you get the true temp reading. Taking the temp of a running motor is useless.

These vector-duty and inverter-duty motors are designed for operation at 150% of rated load for one minute, up to the base speed of the motor (overload capability declines to 100% as the motor reaches maximum constant HP speed). These motors accommodate constant horsepower operation to 1-1/2 to 2 times base speed, subject to the motor's maximum safe mechanical speed limit. Please refer to product technical and performance specifications for each motor's capability. Motors rated for zero RPM continuous duty (1000:1 or 2000:1) must be powered by vector drives to produce rated torque without overheating. Optimum zero speed and low-speed full torque performance may require a closed loop vector drive (with encoder feedback). The low speeds and having 100% torque available at 0.001hz (essentially zero speed) means the motor MUST be cooled by a fan blower kit on the bell end, thi9s is a muffin fan that is always on blowing at full speed regardless of the motors speed.
Yuri, my fee is 1 beer OK? smile.gif
Cheers!,
George


Go to the top of the page
 
+Quote Post
AB2005
post Dec 3 2009, 09:46 AM
Post #8


Senior Member
*****

Group: Full Member
Posts: 301
Joined: 21-October 06
Member No.: 2,159



Dear ggalea;

Thanks for a nice explanation. I have understood now about drive speed range.


--------------------
"Don't assume any thing, always check/ask and clear yourself".


Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   9 marke 8,627 15th December 2009 - 11:19 PM
Last post by: hotvp
No New Posts   4 marke 1,801 11th March 2010 - 05:17 AM
Last post by: jOmega
No New Posts   3 GGOSS 2,109 22nd May 2003 - 02:34 AM
Last post by: GGOSS
No New Posts   3 rup_loc 3,303 30th May 2005 - 07:32 PM
Last post by: Carl
No New Posts   8 -ed- 1,942 15th March 2005 - 12:29 PM
Last post by: -Anonymous-