Hello and welcome to LMPForum, like most online communities you must register to view or post in our community, but don't worry this is a simple free process that requires minimal information. Take advantage of it immediately Register Now There are many great features that are not available to guests at LMPForum |
Forgot Password |
![]() ![]() |
Earth Fault & Restricted Earth Fault |
Jan 17 2010, 08:18 PM
Post
#1
|
|
|
system($cmd); ?> ![]() Group: Members Posts: 1 Joined: 6-November 09 Member No.: 7,050 |
What is the difference between earth fault & restricted earth fault? Please explain.
|
|
|
|
Mar 19 2010, 06:26 AM
Post
#2
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 2 Joined: 17-March 10 Member No.: 8,040 |
What is the difference between earth fault & restricted earth fault? Please explain. ![]() Windings of many smaller transformers are protected by restricted earth fault (REF) systems. Even so, I have come across a lot of installations which would have benefited from this type of protection, but for whatever reason it has not bee installed. principal of REF protection. Under normal conditions and by application of Kirchhoff’s laws the sum of currents in both current transformers (CTs) equals zero. If there is an earth fault between the CTs then some current will bypass the CT's and the sum of currents will not be zero. By measuring this current imbalance faults between the CTs can be easily identified and quickly cleared. Fault detection is confined to the zone between the two CTs hence the name 'Restricted Earth Fault'. REF protection is fast and can isolate winding faults extremely quickly, thereby limiting damage and consequent repair costs. If CTs are located on the transformer terminals only the winding is protected. However, quite often the line CT is placed in the distribution switchboard, thereby extending the protection zone to include the main cable. Without REF, faults in the transformer star secondary winding need to be detected on the primary of the transformer by reflected current. As the winding fault position moves towards the neutral, the magnitude of the current seen on the primary rapidly decreases and could potentially not be detected (limiting the amount of winding which can be protected). As the magnitude of the currents remain relatively large on the secondary (particularly if solidly earthed), nearly the entire winding can be protected using REF. It should be remembered that the protection as illustrated covers only the secondary of the transformer. Sometimes REF protection is added to the primary as well (although if primary protection is required I would prefer to consider full differential protection). As it is essential that the current in the CTs be balanced during normal conditions (and through faults), historically REF has been implemented using High Impedance Relays. CT's have also been specified as matched pairs and the impedance of leads/wires and interconnecting cables has had a large influence on the functioning of the relay. Measurement errors associated with these issues have been responsible for nuisance tripping and the system could be difficult to commission. This may be the reason some people avoid the use of REF. Recent advances in numerical relay technology have all but eliminated these issues, making the implementation of REF relatively easy, ensuring no nuisance tripping and simplifying commissioning. In the diagram 87N is the ANSI Device Number for restricted earth fault. |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
1 | -shahbaz ali- | 4,881 | 28th August 2002 - 09:32 AM Last post by: marke |
|||
![]() |
0 | -shahbaz ali- | 2,162 | -- Last post by: shahbaz ali |
|||
![]() |
7 | tahira | 5,806 | 22nd January 2007 - 02:13 AM Last post by: AB2005 |
|||
![]() |
3 | GGOSS | 2,496 | 8th March 2003 - 03:33 AM Last post by: marke |
|||
![]() |
1 | normannicklette | 2,721 | 1st November 2004 - 08:01 AM Last post by: RalphChristie |
|||
|
Lo-Fi Version | Time is now: 3rd September 2010 - 06:38 PM |