Earth Leakage On Star-delta Close Transition, What causes the Earth Leakage on S/D close transition
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
Gavin
post Jan 9 2008, 01:23 AM
Post #1


Junior Member
**

Group: Members
Posts: 2
Joined: 9-January 08
Member No.: 4,175



I have a system using a star-delta close transition with resistor and capactior starter.

During the starting stage the earth leakage is about 9.6Amp! Is pretty high isn't it? The earth leakage relay is using a differential CT to measure my 3Ph 4 Wire, that is why it can detect the earth leakage during starting. After running it is back to normal zero leakage.

Wire is fine and motor is fine.

What could have causes the leakage current?



Go to the top of the page
 
+Quote Post
chris1373
post Jan 26 2008, 12:51 AM
Post #2


Intermediate Member
***

Group: Full Member
Posts: 31
Joined: 6-September 06
Member No.: 1,906



QUOTE (Gavin @ Jan 9 2008, 01:23 AM) *
I have a system using a star-delta close transition with resistor and capactior starter.


Can you explain the sistem? I dont know it!

Saludos!

Chris.


Go to the top of the page
 
+Quote Post
marke
post Jan 26 2008, 08:47 PM
Post #3


Posting Freak
******

Group: Moderator
Posts: 2,383
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Gavin

There should not be any earth leakage with a closed transition star delta starter.
Earth leakage current would suggest that either the CT is in the wrong place, or there is a fault in the starter.

Chris, for information on the closed transitions star delta starter, look here http://www.lmphotonics.com/star_delta.htm

Best regards,


--------------------


Go to the top of the page
 
+Quote Post
bringit
post Feb 5 2010, 06:31 PM
Post #4



*

Group: Members
Posts: 1
Joined: 5-February 10
Member No.: 7,713



QUOTE (marke @ Jan 27 2008, 04:47 AM) *
Hello Gavin

There should not be any earth leakage with a closed transition star delta starter.
Earth leakage current would suggest that either the CT is in the wrong place, or there is a fault in the starter.

Chris, for information on the closed transitions star delta starter, look here http://www.lmphotonics.com/star_delta.htm

Best regards,


Hello Marke,

I am having the same problem as Gavin. However, I am using a auto-trans (closed transition) starter and there is nothing wrong with the starter.

Any idea why there is an Earth Leakage only during the starting procedure before change over? Why is there such a high earth leakage during starting? The earth leakage was measured using a clamp meter at the earth wire.

Could you kindly advise me on how I can resolve this problem?


Go to the top of the page
 
+Quote Post
marke
post Feb 7 2010, 09:14 AM
Post #5


Posting Freak
******

Group: Moderator
Posts: 2,383
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello bringit

Switching will cause transient and step voltages which can be capacitively coupled to the frame of the motor.
If there is a single impulse at the time of the switching, it is due to the capacitance between cables and earth and the motor windings and the motor frame. This is normal and not a problem.

Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   0 marke 2,036 16th August 2002 - 01:36 AM
Last post by: marke
No New Posts   2 tom 5,511 29th August 2002 - 08:49 AM
Last post by: GGOSS
No New Posts   1 -shahbaz ali- 4,881 28th August 2002 - 09:32 AM
Last post by: marke
No New Posts   0 -shahbaz ali- 2,162 --
Last post by: shahbaz ali
No New Posts   1 gjnj1 2,303 28th September 2002 - 01:32 AM
Last post by: marke


RSS Lo-Fi Version Time is now: 3rd September 2010 - 05:13 PM

Tag cloud:

hosted by : L M Photonics Ltd
LMPhotonics Home  Power factor  Motor Control  Single Phase Motors  Slipring Motors  Motor Starters  Soft Starters  Variable Speed  Energy Savers