Earthing Resistance., Earthing resistance.
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
Nasir
post Oct 18 2007, 04:51 AM
Post #1



*

Group: Members
Posts: 1
Joined: 21-June 07
Member No.: 3,403



I work in oil refinery, Can any body tell me about the earthing resistance. The tranformers, motors and every electrical equipment is earthed for protection purposes. But I just wana ask that what is the standard value(according to NEC or IEC or equivalent) for earthing resistance. The standard use here is 10 ohm but we don't know which standard body recommends this value.



Regards
Nasir.
Go to the top of the page
 
+Quote Post
Matt303
post Oct 23 2007, 04:14 PM
Post #2


Intermediate Member
***

Group: Full Member
Posts: 16
Joined: 26-September 07
Member No.: 3,834



Nasir,

Earthing resistances are used to lessen the earth fault current on a fault. I don't know if there is a standard value for these units but I have fitted them on transformers at 3.3kV and on generator star points.
The rule I use (and seems to be generally applied) is to rate the resistor to limit fault current equal to the current rating of the device (remembering that the voltage is neutral to ground (i.e. dont forget the root 3). The idea is to reduce equipment damage on an earth fault. You ned to select a rating for the resistor that will allow it to pass current for enough time to operate the protection (they are usually rated for 3s or 10s for a particular temperature rise). They get very hot if a fault occurs so place them somewhere where nobody might accidentally touch them.
I have never added these units at LV but at 3.3kV and above. I think that the current can be limited to greater extent if necessary for generators and motors which are not very earth fault tolerant. Clearly the fault must be such that the protection can recognise it and on a machine or transformer there is normally some sort of unit protection like restricted earth fault to allow a more sensitive setting.
Often when fitted to a distribution transormer star point in addition to the restricted earth fault protection a standby earth fault protection is also fitted which is a single element overcurrent relay designed as back up protection.
I've attached a file that might be useful

Regards

Matt
Attached File(s)
Attached File  specifying_ners.pdf ( 56.32K ) Number of downloads: 7
 
Go to the top of the page
 
+Quote Post
master.spicy
post Sep 18 2008, 06:16 AM
Post #3



*

Group: Members
Posts: 1
Joined: 18-September 08
Member No.: 4,821



As per IEEE 80 and NFPA, earthing resistance should be less than 5 ohm for LV and LT systems, and should be less than 1 ohm for HV and EHV systems. during calculations also we have to consider step and touch voltages for HV systems. the standard that mentions is IEEE 80. Please make a note of the same.
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   5 tahira 1,468 15th January 2003 - 06:01 PM
Last post by: marke
No New Posts   1 Greg 703 5th January 2004 - 07:10 PM
Last post by: marke
No New Posts   3 asgkrishnan 1,206 24th February 2006 - 06:42 AM
Last post by: marke
No New Posts   0 chaterpilar 624 7th June 2006 - 03:40 AM
Last post by: chaterpilar
No New Posts   1 Darren 594 21st June 2006 - 07:33 PM
Last post by: marke



RSS Lo-Fi Version Time is now: 21st November 2008 - 06:31 PM
hosted by : L M Photonics Ltd