This is my first post and I can tell from reading the other posts that in regards to technical knowledge, I am far behind most people on this site...so please speak slowly.

Situation: Have generator that runs multiple conveyors as well as other asphalt machinery.

Question: If we use custom made capacitors to correct the Power Factor in circuit with each motor running off the generator. Then at a later time add additional conveyors (motors), will this effect the Power Factor of the motors we previously optimized.

Thanks,


Luke



Go to the top of the page
 
+Quote Post
marke
post Dec 4 2007, 04:48 AM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,099
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello LukeC

Welcome to the forum.

There are two types of power factor, displacement power factor and distortion power factor. Typically, most people considering power factor, are concerned with displacement power factor only.

Every motor has a component of the current drawn which is called the magnetizing current. This is a characteristic of that particular motor and varies between motors. The magnetizing current is constant and independent of load.
The magnetizing current is an inductive current and would generally be between 20% and 50% of the motor rated current.
When the motor operates open shaft, it is essentially the magnetizing current that is drawn.

Power factor correction capacitors are applied to the circuit to cancel out the inductive magnetizing current of the motor. If you add the correct amount of correction, then the power factor would typically be greater than 0.95. If you then add additional motors, the total magnetizing current will be increased and so the capacitor current needs to be increased also to give good correction.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   1 -Billy- 3,119 6th May 2002 - 10:22 PM
Last post by: marke
No New Posts   0 Asad 2,176 11th May 2002 - 03:24 AM
Last post by: Asad
No new   60 marke 17,881 27th March 2008 - 05:44 AM
Last post by: Macabenta
No New Posts   2 Itos 2,174 13th August 2002 - 03:40 PM
Last post by: nadeem1990pk
No New Posts   4 Itos 1,893 24th June 2002 - 04:02 AM
Last post by: Itos



RSS Lo-Fi Version Time is now: 21st November 2008 - 10:28 PM
hosted by : L M Photonics Ltd