Generator synchronisation |
![]() ![]() |
Generator synchronisation |
Dec 20 2005, 02:46 PM
Post
#1
|
|
![]() Member ![]() ![]() ![]() ![]() Group: Full Member Posts: 165 Joined: 3-September 04 Member No.: 861 |
We are using 5 CATs 1600kva in sync.
Load sharing is done by woodward load sharing module. We notice that the synchronisation is intact till 50% of capacity of generator and the synchronisation is lost after any furthur load is applied and generators trip. What can cause this behaviour? chaterpilar |
|
|
|
Dec 24 2005, 01:42 PM
Post
#2
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Members Posts: 16 Joined: 10-November 05 Member No.: 1,276 |
This appears to be due to wrong droop and load limit setttings on the Governors
|
|
|
|
![]() ![]() |