High Current Reading
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
NEMotorTech
post Jun 29 2009, 04:07 PM
Post #1



*

Group: Members
Posts: 1
Joined: 29-June 09
Member No.: 5,688



We have a motor on the bench that draws 0.6 amps (no load) in each phase with 460V applied. When voltage increases to 473V the current increases to 0.81 amps and when 493V current is 0.93 amps that is above FLA of motor.

The applied voltage is within the +/- 10% of the motor nameplate. Would this increase in current be due to voltage saturation in the stator or maybe the air gap between stator and rotor is not correct?


Go to the top of the page
 
+Quote Post
Clayts
post Jul 1 2009, 07:12 AM
Post #2


Intermediate Member
***

Group: Full Member
Posts: 38
Joined: 7-June 06
From: New Zealand
Member No.: 1,554




General rule of thumb is the NLA will be half that of the rated FLA for a two pole. If it's a 4 pole it will be smaller still. But why are you ramping up voltage beyond what it is designed for? I can't really answer your saturation question. From experience, people like to say that motors are over saturated when the preliminary test results are inconclusive. Maybe somebody else can answer that one!.



Go to the top of the page
 
+Quote Post
yuri
post Jul 1 2009, 06:30 PM
Post #3


Member
****

Group: Full Member
Posts: 78
Joined: 13-June 09
Member No.: 5,502



HI.
460 V is its nameplate voltage? What is its temperature after 1 hour of work on 460V and without load? (and what has been ambient temp by that?)


Go to the top of the page
 
+Quote Post
volt
post Jul 3 2009, 10:27 AM
Post #4


Junior Member
**

Group: Full Member
Posts: 5
Joined: 2-July 09
Member No.: 5,725



Well, its not the same if you applied 460 V and 500 V, imagine a situation like this: you have a resistor with ratings 2 ohms and you applied voltage about 4 volts, the current draw is 2 amps, if you increase voltage to 8 volts, current ramps up to 4 amps, the same thing is with your motor, if you applied 460 volts it vill draw 0.6 amps, if you increase voltage, the resistance of motor windings stay same and the current ramps up. BTW dont increase voltage of motor, you will burn out the windings because they are designed for .6 amps not for .93


Go to the top of the page
 
+Quote Post
marke
post Jul 4 2009, 04:37 AM
Post #5


Posting Freak
******

Group: Moderator
Posts: 2,383
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello NEMotorTech

There are two major components of the current drawn by a motor.
1. The magnetizing current
2. The work current.

The magnetizing current is the current that is required to develop the flux in the gap and is determined by stator turns, the stator design and the voltage applied.

Small motors are typically designed to operate with a much higher flux density than large motors.
With the higher flux density, the ratio of magnetizing current to rated current reduces.
Large three phase motors will typically have a magnetizing current in the order of 20 - 25% of the rated current, but small motors will commonly be as high as 60%.
If the flux density is high, a small change in applied voltage will result in a large change in magnetizing current. This is due to the saturation of the iron in the stator. This results in a dramatic increase in the iron losses and can cause the motor to overheat and fail.

As the voltage is increased, the magnetizing current also increases.
As the voltage is increased, the work current reduces.

The motor that you describe is operating at saturation.

Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post
yuri
post Jul 4 2009, 08:08 PM
Post #6


Member
****

Group: Full Member
Posts: 78
Joined: 13-June 09
Member No.: 5,502



Hello Mark!
Glad to here from you and read your posts again.

The original poster has made the point that the motor operated within the allowable voltage range and by that it overpassed the FLA. That is, nominal voltage being 460, allowable +/- 10 %, there was applied + 8% (if I remember good), by that, FLA was overpassed - without any load.

Do I understood you right that the nameplate states active current(s) ? Thus, there measured 0.9 apparent but, let's say, there was only 0.7A active current, which still was less than FLA?

The best regards.
Yuri


Go to the top of the page
 
+Quote Post
marke
post Jul 4 2009, 09:06 PM
Post #7


Posting Freak
******

Group: Moderator
Posts: 2,383
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Yuri

I would suggest that the +/- 10% on voltage is optimistic on a motor this size. Small motors are overfluxed by design and so are very sensitive to an increase in voltage.
Larger motors operate at a lower flux density and so are more tolerant of an increase in voltage to a certain point.
If the magnetising current was say 70% of the rated current, then an increase in load current from zero would have no influence on the measured current until the load current was significant relative to the magnetizing current. The two currents are at phase quadrature so it is vector adition rather than magnitude addition.

The current rating is the total current as you would read with an ameter, not the individual work or magnetizing currents.

Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post
yuri
post Jul 5 2009, 08:24 AM
Post #8


Member
****

Group: Full Member
Posts: 78
Joined: 13-June 09
Member No.: 5,502



Thank you, Mark.

My best regards,
Yuri.


Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   1 -shahbaz ali- 4,881 28th August 2002 - 09:32 AM
Last post by: marke
No New Posts   0 -shahbaz ali- 2,162 --
Last post by: shahbaz ali
No New Posts   10 theDOG 2,740 25th September 2002 - 10:39 AM
Last post by: marke
No New Posts   1 tom 5,631 15th August 2003 - 04:00 PM
Last post by: merajdab
No New Posts   0 GGOSS 1,183 29th November 2002 - 05:26 AM
Last post by: GGOSS


RSS Lo-Fi Version Time is now: 3rd September 2010 - 05:17 PM
hosted by : L M Photonics Ltd
LMPhotonics Home  Power factor  Motor Control  Single Phase Motors  Slipring Motors  Motor Starters  Soft Starters  Variable Speed  Energy Savers