Maximum Frequency
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
Cesar
post Jan 25 2010, 10:17 PM
Post #1



*

Group: Members
Posts: 1
Joined: 25-January 10
Member No.: 7,618



I have the following application:

Motor: 300Hp/2000V/40A/60Hz

VSD: 520KVA@480V

Power Supply: 50Hz/380V

What is the maximum frequency I can run the motor ?


Go to the top of the page
 
+Quote Post
yuri
post Jan 29 2010, 11:27 PM
Post #2


Member
****

Group: Full Member
Posts: 78
Joined: 13-June 09
Member No.: 5,502



QUOTE (Cesar @ Jan 25 2010, 11:17 PM) *
I have the following application:

Motor: 300Hp/2000V/40A/60Hz

VSD: 520KVA@480V

Power Supply: 50Hz/380V

What is the maximum frequency I can run the motor ?

Hello.
Maybe 100?
Only 2 questions:
Where 2000 V will be taken from?
What the 480V VSD will be doing in the application ?


Go to the top of the page
 
+Quote Post
marke
post Jan 30 2010, 07:18 AM
Post #3


Posting Freak
******

Group: Moderator
Posts: 2,383
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Cesar

The maximum frequency that you can run the motor is dependent on two major considerations.

1. The maximum speed that the bearings can operate at. Check with the motor manufacturer or bearing supplier.

2. The speed torque curve of the driven load. As you change the frequency, you change the power capacity of the motor.
At frequencies below the rated frequency of the motor, the voltage applied to the motor must be reduced proportional to the frequency reduction. This results in constant torque below rated frequency and ad power is torque times speed, the power capacity of the motor reduces with reducing frequency.
Above rated frequency, it is normal for the voltage to be limited to rated voltage by the magnitude of the supply voltage. This reduces the flux in the iron as the frequency is increased and reduces the torque output of the motor. bove rated frequency, the motor can deliver rated power.
As the speed of the load is increased, the torque required to drive the load typically increases.
The maximum frequency may be limited by the torque requirement of the load and the torque capacity of the motor.

Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   1 marke 1,509 19th May 2002 - 05:59 AM
Last post by: marke
No New Posts   2 milliamp 3,055 13th September 2002 - 05:47 AM
Last post by: marke
No New Posts   2 gogo 1,174 22nd May 2003 - 02:19 AM
Last post by: GGOSS
No New Posts   6 Igneous 2,427 8th September 2003 - 01:23 AM
Last post by: GGOSS
No New Posts   0 hemant 2,544 4th March 2004 - 03:30 PM
Last post by: hemant


RSS Lo-Fi Version Time is now: 3rd September 2010 - 05:07 PM
hosted by : L M Photonics Ltd
LMPhotonics Home  Power factor  Motor Control  Single Phase Motors  Slipring Motors  Motor Starters  Soft Starters  Variable Speed  Energy Savers