Mccb Seetings
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
jameel
post Feb 3 2009, 02:29 PM
Post #1



*

Group: Members
Posts: 1
Joined: 3-February 09
Member No.: 5,124



WE are using a 63A MCCB(SIEMENS MAKE) for one of the feeder in LV substation panel.It is supplying to a lighting & power socket DB.Settings in the MCCB is Ir = 63 * 1 , Isd = 8 times of Ir , tsd = 0.5 sec( I2 t off).
Sometimes this MCCB is tripping .But no trip in DB MCB.
Can anybody tell me reason ?
From where i can know about the MCCB settings?


Go to the top of the page
 
+Quote Post
pft77
post Jun 20 2009, 02:14 AM
Post #2



*

Group: Members
Posts: 1
Joined: 10-June 09
Member No.: 5,462



QUOTE (jameel @ Feb 3 2009, 10:29 PM) *
WE are using a 63A MCCB(SIEMENS MAKE) for one of the feeder in LV substation panel.It is supplying to a lighting & power socket DB.Settings in the MCCB is Ir = 63 * 1 , Isd = 8 times of Ir , tsd = 0.5 sec( I2 t off).
Sometimes this MCCB is tripping .But no trip in DB MCB.
Can anybody tell me reason ?
From where i can know about the MCCB settings?


do you have current injector ?

if you do, you may test the mccb by injecting 63A.


Go to the top of the page
 
+Quote Post
jsl
post Sep 14 2009, 10:16 PM
Post #3


Junior Member
**

Group: Members
Posts: 3
Joined: 14-September 09
Member No.: 6,526



QUOTE (jameel @ Feb 3 2009, 11:29 PM) *
WE are using a 63A MCCB(SIEMENS MAKE) for one of the feeder in LV substation panel.It is supplying to a lighting & power socket DB.Settings in the MCCB is Ir = 63 * 1 , Isd = 8 times of Ir , tsd = 0.5 sec( I2 t off).
Sometimes this MCCB is tripping .But no trip in DB MCB.
Can anybody tell me reason ?
From where i can know about the MCCB settings?



there could be many reasons for tripping
1 if the cummulative output current (all lights and sockets etc) exceeds 63 amps
2 if your had a circuit that required a large inrush current (motor or transformer etc)
3


Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts 9 AB2005 31,136 3rd March 2010 - 11:01 AM
Last post by: AB2005
No New Posts   3 Mark Monson 3,222 12th November 2007 - 08:40 PM
Last post by: marke


RSS Lo-Fi Version Time is now: 13th March 2010 - 09:34 PM
hosted by : L M Photonics Ltd
LMPhotonics Home  Power factor  Motor Control  Single Phase Motors  Slipring Motors  Motor Starters  Soft Starters  Variable Speed  Energy Savers