Modbus Rtu With Danfoss Fc102
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
Marcel
post Jun 1 2009, 01:08 PM
Post #1



*

Group: Members
Posts: 1
Joined: 1-June 09
Member No.: 5,419



Hi,

I'm trying to read and write some parameters from a Danfoss FC102 with a MODBUS RTU protocoll.
Unfortunatly i don't have the list with available MODBUS parameters for the Danfoss FC102.

Can someboby tell me where i can find the MODBUS-list? The Danfoss website did not help me out.

Regards,
Marcel


Go to the top of the page
 
+Quote Post
marke
post Jun 1 2009, 04:07 PM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,336
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Marcel

Welcome to the forum.

I presume that the FC102 is the same as the FC202, in which case the information in the manuals is a little unclear and in some cases, misleading.

You must use MODBUS 6 digit addressing if you want to access all the registers, and typically the upper registers are the ones that you will want to read and write.

The addresses are made up of taking the Danfoss function number, multiplying by 1000 and adding 400000.
For example, to access 16.03, you take 16.03 x 1000 = 16030 then add 400000 to get 416030 and that is the six digit addressing.

If you do not have six digit addressing available, and your plc is not fully 5 digit compliant in that it lets you exceed 49999, then you can add 40000 instead so 16.03 would become 56030.

The control word can be accessed at 50.00 so with 6 digit addressing, this becomes 450000.

The only other issue that I have found is that some 16 bit data needs to be accessed as 32 or you get an error.
I would suggest adding one data field at a time to prove single word or double word access.

Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   2 marke 3,483 17th March 2006 - 10:37 AM
Last post by: omron
No New Posts   8 rusman 1,755 26th February 2007 - 06:13 PM
Last post by: marke
No New Posts   6 fede00 1,650 2nd March 2007 - 03:25 AM
Last post by: marke
No New Posts   0 marke 1,279 24th April 2007 - 06:19 AM
Last post by: marke
No New Posts   3 Steven1984 2,546 7th April 2008 - 07:17 AM
Last post by: Steven1984


RSS Lo-Fi Version Time is now: 14th March 2010 - 03:33 PM

Tag cloud:

hosted by : L M Photonics Ltd
LMPhotonics Home  Power factor  Motor Control  Single Phase Motors  Slipring Motors  Motor Starters  Soft Starters  Variable Speed  Energy Savers