Motor Current Varying Without Load
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
AB2005
post Nov 20 2009, 05:35 AM
Post #1


Senior Member
*****

Group: Full Member
Posts: 277
Joined: 21-October 06
Member No.: 2,159



Dear Friends;

I have been facing a problem with a 10KW, 22A, 66HZ, 380V VFD compatible motor. The motor rotates a shaft having slitting knifes. First time it happened that motor current increased up to 34A. During checking I found that at 0-20HZ, its current was near about 34A (without load) and as speed increased current decreased at 13A. There was no any jamming in rotor moment found. We re-winded the motor, replaced the bearings, connected the motor at direct line, checked it current without load and found the same behavior as written above.
Any bode have any idea? For me, this is a rotor problem but it looked like ok.


--------------------
"Don't assume any thing, always check/ask and clear yourself".


Go to the top of the page
 
+Quote Post
yuri
post Nov 20 2009, 05:45 PM
Post #2


Member
****

Group: Full Member
Posts: 78
Joined: 13-June 09
Member No.: 5,502



Hello.
I support your suspicion of the rotor. It happens - laminations insulation (there should be some although all looks so monolithic) degrades, some bars get distorted, rotor may be slightly shifthed along the axe, and the motor would draw more current and heat up. With current differences 34 and 13 - it must be very hot.
The rewinders, at a good repairing shop should have the appliance that measures rotor losses - so it was some time ago, am not sure what they use now. It's like a half-transformer, into which you put the rotor (thus forming its "second winding"). You may want to bring the rotor to them.
Best regards.


Go to the top of the page
 
+Quote Post
marke
post Nov 20 2009, 06:52 PM
Post #3


Posting Freak
******

Group: Moderator
Posts: 2,336
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello AB2005

It sounds to me as though the V/Hz ratio is wrong at the low speeds.
Typically this is due to a voltage or torque boost setting, or a 60Hz motor programmed in as a 50 Hz motor.
You say that the motor is a 66Hz motor. I am not sure if this is a typo or actually a 66Hz motor.
In this case, the motor data must be programmed in as a 66Hz motor. If you set it as a 60Hz motor, you will overflux the motor and the current will be too high. At higher speeds, the VFD may be voltage limiting and this will reduce the flux.

Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post
AB2005
post Nov 24 2009, 06:10 AM
Post #4


Senior Member
*****

Group: Full Member
Posts: 277
Joined: 21-October 06
Member No.: 2,159



Yes, problem has been found in rotor which winding has shorted.

Thanks to friends for replying.


--------------------
"Don't assume any thing, always check/ask and clear yourself".


Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   2 GGOSS 4,666 28th July 2003 - 05:46 AM
Last post by: GGOSS
No New Posts   2 marke 6,831 4th July 2009 - 05:27 AM
Last post by: marke
No New Posts   0 marke 5,318 11th June 2002 - 10:34 PM
Last post by: marke
No New Posts   1 marke 3,828 7th December 2009 - 10:32 AM
Last post by: Broshi
No New Posts   0 marke 2,770 12th June 2002 - 09:24 AM
Last post by: marke


RSS Lo-Fi Version Time is now: 14th March 2010 - 11:09 PM
hosted by : L M Photonics Ltd
LMPhotonics Home  Power factor  Motor Control  Single Phase Motors  Slipring Motors  Motor Starters  Soft Starters  Variable Speed  Energy Savers