sir
we have in our Motor control centre motors of various capacities running.The starters are of DOL type and type 2 coordinated.we dont have ground fault protection for each motors. in case of a insulation failure in any of the motors the incoming feeder to the mcc trips and the whole section gets affected.The fuses in the motor feeder also fails but the incomer breaker motor control centre mcc trips very fast. how to isolate the faulty motor alone ram |
|
|
|
Mar 18 2007, 06:43 AM
Post
#2
|
|
![]() Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 644 Joined: 22-February 03 From: USA, California Member No.: 285 |
You need to perform a system coordination study, a process by which an electrical engineer determines the proper fusing and breaker trip settings to ensure that a fault is interrupted at the lowest possible level.
-------------------- "He's not dead, he's just pinin' for the fjords!"
|
|
|
|
Mar 24 2007, 02:11 PM
Post
#3
|
|
|
Member ![]() ![]() ![]() ![]() Group: Full Member Posts: 51 Joined: 17-December 05 Member No.: 1,308 |
QUOTE(jraef @ Mar 18 2007, 12:13 PM) [snapback]5739[/snapback] You need to perform a system coordination study, a process by which an electrical engineer determines the proper fusing and breaker trip settings to ensure that a fault is interrupted at the lowest possible level. thanks sir since we have different ratings of motor is it possible to corelate all the fuse ratings with the breaker.Also i understand that whenever there is problem in the motor(ground fault) the overload relay should trip the contactor . on the otherhand if there is problem in the cable leading to motor the fuse should blow and the breaker should trip and the contactor is not supposed to open. your comments ram |
|
|
|
Mar 24 2007, 11:17 PM
Post
#4
|
|
![]() Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 644 Joined: 22-February 03 From: USA, California Member No.: 285 |
An overload relay is not designed to trip on a ground fault specifically. It might trip if the ground current exceeds the setting, but often times if the ground fault has high resistance or acring, the ground current will be too low to be picked up by the OL relay. The best method is to use a ground fault relay of some sort, or possibly use a solid state OL relay that includes residual ground fault protection. Some do, some do not. You need to check for sure.
-------------------- "He's not dead, he's just pinin' for the fjords!"
|
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
2 | GGOSS | 2,525 | 28th July 2003 - 05:46 AM Last post by: GGOSS |
|||
![]() |
0 | marke | 2,672 | 11th June 2002 - 10:32 PM Last post by: marke |
|||
![]() |
0 | marke | 2,115 | 11th June 2002 - 10:34 PM Last post by: marke |
|||
![]() |
0 | marke | 1,846 | 11th June 2002 - 10:42 PM Last post by: marke |
|||
![]() |
0 | marke | 1,893 | 12th June 2002 - 09:24 AM Last post by: marke |
|||
|
Lo-Fi Version | Time is now: 8th September 2008 - 12:39 AM |