Hello and welcome to LMPForum, like most online communities you must register to view or post in our community, but don't worry this is a simple free process that requires minimal information. Take advantage of it immediately Register Now There are many great features that are not available to guests at LMPForum |
Forgot Password |
![]() ![]() |
Motor Protection Numerical Relay, you have a separate numerical relay for LV motor&HTmotor. |
Feb 11 2008, 05:55 PM
Post
#1
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 2 Joined: 22-April 07 Member No.: 3,191 |
you have separate numerical relay for LV motor &HT motor.Can you use the LV motor numerical relay for HT motor protection without any modificationHT motor protection
|
|
|
|
Mar 21 2008, 05:09 PM
Post
#2
|
|
|
Junior Member ![]() ![]() Group: Full Member Posts: 7 Joined: 19-March 08 Member No.: 4,399 |
I dont see any difference b/w LT and HT motor protection. I think same relay can be used following to be considered a) If u use the low imp. scheme for earth fault then u may have to recalculate the stabilizing resistor value c) CT PT ration as per the new set up |
|
|
|
![]() ![]() |