Hello and welcome to LMPForum, like most online communities you must register to view or post in our community, but don't worry this is a simple free process that requires minimal information. Take advantage of it immediately Register Now There are many great features that are not available to guests at LMPForum |
Forgot Password |
![]() ![]() |
Motor Starting Problems |
Dec 6 2009, 06:22 PM
Post
#1
|
|
|
system($cmd); ?> ![]() Group: Members Posts: 1 Joined: 6-December 09 Member No.: 7,267 |
Hi, I am having problems with a 230v 3ph 10hp baldor motor on a compressor.
The problem is that it burns up the contacts (blows them apart). I have ran it on the contact starter that came with it for a few months and I started having problems with a 40 amp contactor so i switched to a 50 amp and it lasted about a week. I checked voltage at the panel and it was 240 across the phases. The motor requires 28 amps, the latest suggestion was to go tos nema 2 rated box but it will cost 2 times the price of the motor! Any help will be much appreciated. Thanks Fredster |
|
|
|
Dec 12 2009, 08:16 AM
Post
#2
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 3 Joined: 22-November 09 Member No.: 7,159 |
welcome
I think , your problem with contactor ( it is not good ) , if the voltage 240 , because this voltage is normal but when voltage become high , in that time you can to drop it by : 1- by control on the tap changer of transformer 2- by using stabilizer( it cost ) and thanks |
|
|
|
Dec 12 2009, 09:52 AM
Post
#3
|
|
|
Member ![]() ![]() ![]() ![]() Group: Full Member Posts: 80 Joined: 13-June 09 Member No.: 5,502 |
[quote name='fredster' date='Dec 6 2009, 07:22 PM' post='10534']
Hi, I am having problems with a 230v 3ph 10hp baldor motor on a compressor. The problem is that it burns up the contacts (blows them apart). I have ran it on the contact starter that came with it for a few months and I started having problems with a 40 amp contactor so i switched to a 50 amp and it lasted about a week. I checked voltage at the panel and it was 240 across the phases. The motor requires 28 amps, the latest suggestion was to go tos nema 2 rated box but it will cost 2 times the price of the motor! Any help will be much appreciated. Thanks Fredster [/quoteHello/ Hello. Maybe the compressor is needing now an overhaul, or it now is made to start with a higher dP accros it (such as the starting differential may have been decreased for instance). |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
2 | GGOSS | 5,175 | 28th July 2003 - 05:46 AM Last post by: GGOSS |
|||
![]() |
2 | marke | 7,781 | 4th July 2009 - 05:27 AM Last post by: marke |
|||
![]() |
0 | marke | 6,118 | 11th June 2002 - 10:34 PM Last post by: marke |
|||
![]() |
1 | marke | 4,342 | 7th December 2009 - 10:32 AM Last post by: Broshi |
|||
![]() |
0 | marke | 3,038 | 12th June 2002 - 09:24 AM Last post by: marke |
|||
|
Lo-Fi Version | Time is now: 10th September 2010 - 02:46 PM |