Hello and welcome to LMPForum, like most online communities you must register to view or post in our community, but don't worry this is a simple free process that requires minimal information. Take advantage of it immediately Register Now There are many great features that are not available to guests at LMPForum |
Forgot Password |
![]() ![]() |
Motor Starting, DOL |
Jun 14 2008, 07:04 AM
Post
#1
|
|
|
Member ![]() ![]() ![]() ![]() Group: Full Member Posts: 187 Joined: 16-August 05 Member No.: 1,186 |
Hi,
I am commissioning a 90 k W 400/600 V 50 Hz motor DOL starting. The motor circuit breaker tripped instatantaneously when the motor is started. I measured an inrush current of 1400 A by the Fluke 435 analyser. The magnetic setting on the motor breaker is 2400 Amps. I suspect the motor breaker is faulty. The rated current of the motor is 160 Amps and if I assume a LRC of 900 % i.e 1440 Amps, then the motor breaker should have been able to start the motor. I have also connected the motor in star and it drew 90 Amps per phase and I assume the motor is OK. Any comment ? Bob |
|
|
|
Jun 14 2008, 08:27 AM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,383 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello Bob
Yes, you are correct with your currents, except that when you DOL start, there is an initial infush curent which can last for a cycle or two which can be more than two times the LRC of the motor. If the magnetic trip is fast enough, it could be operating on the inrush current rather than the LRC. The inrush current is the initial current that establishes the magnetic field which then limits the current to the LRC. Perhaps the Fluke is not fast enough to pick it up. - could be a settings thing. Best regards, Mark -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Jun 15 2008, 06:23 AM
Post
#3
|
|
|
Member ![]() ![]() ![]() ![]() Group: Full Member Posts: 187 Joined: 16-August 05 Member No.: 1,186 |
Hi Marke,
Thanks for your usual prompt and expert reply. I have replaced the motor breaker with a similar one and the motor startS well. Regards. Bob |
|
|
|
Aug 8 2008, 09:12 AM
Post
#4
|
|
|
Junior Member ![]() ![]() Group: Full Member Posts: 5 Joined: 6-August 08 Member No.: 4,724 |
Hello Bob Yes, you are correct with your currents, except that when you DOL start, there is an initial infush curent which can last for a cycle or two which can be more than two times the LRC of the motor. If the magnetic trip is fast enough, it could be operating on the inrush current rather than the LRC. The inrush current is the initial current that establishes the magnetic field which then limits the current to the LRC. Perhaps the Fluke is not fast enough to pick it up. - could be a settings thing. Best regards, Mark Hi again Mr. Mark, I have read several replies of yours to our co-members in this forum; And I'm quite impressed with the way you handle questions. Regarding the "inrush current which is greater than the LRC" can you kindly give me reference for it. I would like to know more....=) Thanks in advance. Best Regards, Animna |
|
|
|
Aug 9 2008, 07:39 AM
Post
#5
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,383 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello Anima
Thank you for your comments. When you first apply full voltage to an induction motor, there is a current surge called the inrush current. This is a very short burst of current and is the current required to establish the flux in the iron.Once the iron is fluxed, the current drops down to the locked rotor current where the current is determined by the effective rotor impedance, leakage reactance and stator impedance. When you apply power to a transformer, you also get an inrush current which is the same sort of current. - the current required to establish the flux in the iron. Best regards, Mark. -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Aug 10 2008, 02:06 AM
Post
#6
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 4 Joined: 24-July 08 Member No.: 4,701 |
Hello Bob
Yes, you are correct with your currents, except that when you DOL start, there is an initial infush curent which can last for a cycle or two which can be more than two times the LRC of the motor. If the magnetic trip is fast enough, it could be operating on the inrush current rather than the LRC. The inrush current is the initial current that establishes the magnetic field which then limits the current to the LRC. Perhaps the Fluke is not fast enough to pick it up. - could be a settings thing. Best regards, Mark |
|
|
|
Aug 10 2008, 02:16 AM
Post
#7
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 4 Joined: 24-July 08 Member No.: 4,701 |
Hello Marke,
I appreciate your answer also on that subject. Can you help clarify the following. I have experience with NEMA Motors, and not much experience with IEC applications. Recently came across " Absorbed load " and on review became confused, perhaps you can solve the confusion. load factor = absorbed load / motor rating static load. Thanks Jeff |
|
|
|
Aug 10 2008, 02:34 AM
Post
#8
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,383 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hi Jeff
That is not a term that I use, but I expect that the "absorbed load" is the shaft power as opposed to the input power. IEC motors are rated in maximum shaft power. Many people confuse this with the electrical input power and this is higher as it includes the motor losses. A 10KW motor has a shaft power of 10KW and in input power at rated load of 11.5KW Have a good day, Best regards, Mark. -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Aug 10 2008, 11:28 AM
Post
#9
|
|
|
Junior Member ![]() ![]() Group: Full Member Posts: 5 Joined: 6-August 08 Member No.: 4,724 |
Hello Anima Thank you for your comments. When you first apply full voltage to an induction motor, there is a current surge called the inrush current. This is a very short burst of current and is the current required to establish the flux in the iron.Once the iron is fluxed, the current drops down to the locked rotor current where the current is determined by the effective rotor impedance, leakage reactance and stator impedance. When you apply power to a transformer, you also get an inrush current which is the same sort of current. - the current required to establish the flux in the iron. Best regards, Mark. Dear Mr. Mark, Thanks for your expertise. You have respect. Best Regards, animna |
|
|
|
Aug 10 2008, 05:09 PM
Post
#10
|
|
|
Member ![]() ![]() ![]() ![]() Group: Full Member Posts: 187 Joined: 16-August 05 Member No.: 1,186 |
Dear Mark,
I understand that the LRC is a function of the characteristics of the motor. However, the inrush current is directly dependent on the mode of starting and applied voltage. Am I right ? Best regards. Bob |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
2 | GGOSS | 5,167 | 28th July 2003 - 05:46 AM Last post by: GGOSS |
|||
![]() |
2 | marke | 7,765 | 4th July 2009 - 05:27 AM Last post by: marke |
|||
![]() |
0 | marke | 6,108 | 11th June 2002 - 10:34 PM Last post by: marke |
|||
![]() |
1 | marke | 4,332 | 7th December 2009 - 10:32 AM Last post by: Broshi |
|||
![]() |
0 | marke | 3,031 | 12th June 2002 - 09:24 AM Last post by: marke |
|||
|
Lo-Fi Version | Time is now: 7th September 2010 - 04:41 PM |