Motor Starting, DOL
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
bob
post Jun 14 2008, 07:04 AM
Post #1


Member
****

Group: Full Member
Posts: 187
Joined: 16-August 05
Member No.: 1,186



Hi,

I am commissioning a 90 k W 400/600 V 50 Hz motor DOL starting. The motor circuit breaker tripped instatantaneously when the motor is started. I measured an inrush current of 1400 A by the Fluke 435 analyser. The magnetic setting on the motor breaker is 2400 Amps. I suspect the motor breaker is faulty. The rated current of the motor is 160 Amps and if I assume a LRC of 900 % i.e 1440 Amps, then the motor breaker should have been able to start the motor. I have also connected the motor in star and it drew 90 Amps per phase and I assume the motor is OK.
Any comment ?

Bob


Go to the top of the page
 
+Quote Post
marke
post Jun 14 2008, 08:27 AM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,383
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Bob

Yes, you are correct with your currents, except that when you DOL start, there is an initial infush curent which can last for a cycle or two which can be more than two times the LRC of the motor. If the magnetic trip is fast enough, it could be operating on the inrush current rather than the LRC.
The inrush current is the initial current that establishes the magnetic field which then limits the current to the LRC.
Perhaps the Fluke is not fast enough to pick it up. - could be a settings thing.

Best regards,
Mark


--------------------


Go to the top of the page
 
+Quote Post
bob
post Jun 15 2008, 06:23 AM
Post #3


Member
****

Group: Full Member
Posts: 187
Joined: 16-August 05
Member No.: 1,186



Hi Marke,

Thanks for your usual prompt and expert reply. I have replaced the motor breaker with a similar one and the motor startS well.

Regards.

Bob


Go to the top of the page
 
+Quote Post
animna
post Aug 8 2008, 09:12 AM
Post #4


Junior Member
**

Group: Full Member
Posts: 5
Joined: 6-August 08
Member No.: 4,724



QUOTE (marke @ Jun 14 2008, 06:27 PM) *
Hello Bob

Yes, you are correct with your currents, except that when you DOL start, there is an initial infush curent which can last for a cycle or two which can be more than two times the LRC of the motor. If the magnetic trip is fast enough, it could be operating on the inrush current rather than the LRC.
The inrush current is the initial current that establishes the magnetic field which then limits the current to the LRC.
Perhaps the Fluke is not fast enough to pick it up. - could be a settings thing.

Best regards,
Mark




Hi again Mr. Mark,

I have read several replies of yours to our co-members in this forum; And I'm quite impressed with the way you handle questions.
Regarding the "inrush current which is greater than the LRC" can you kindly give me reference for it. I would like to know more....=)

Thanks in advance.

Best Regards,
Animna


Go to the top of the page
 
+Quote Post
marke
post Aug 9 2008, 07:39 AM
Post #5


Posting Freak
******

Group: Moderator
Posts: 2,383
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Anima

Thank you for your comments.

When you first apply full voltage to an induction motor, there is a current surge called the inrush current. This is a very short burst of current and is the current required to establish the flux in the iron.Once the iron is fluxed, the current drops down to the locked rotor current where the current is determined by the effective rotor impedance, leakage reactance and stator impedance.

When you apply power to a transformer, you also get an inrush current which is the same sort of current. - the current required to establish the flux in the iron.

Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post
Jeff Millar
post Aug 10 2008, 02:06 AM
Post #6


Junior Member
**

Group: Members
Posts: 4
Joined: 24-July 08
Member No.: 4,701



QUOTE (marke @ Jun 14 2008, 11:27 AM) *
Hello Bob

Yes, you are correct with your currents, except that when you DOL start, there is an initial infush curent which can last for a cycle or two which can be more than two times the LRC of the motor. If the magnetic trip is fast enough, it could be operating on the inrush current rather than the LRC.
The inrush current is the initial current that establishes the magnetic field which then limits the current to the LRC.
Perhaps the Fluke is not fast enough to pick it up. - could be a settings thing.

Best regards,
Mark


Go to the top of the page
 
+Quote Post
Jeff Millar
post Aug 10 2008, 02:16 AM
Post #7


Junior Member
**

Group: Members
Posts: 4
Joined: 24-July 08
Member No.: 4,701



Hello Marke,

I appreciate your answer also on that subject.

Can you help clarify the following. I have experience with NEMA Motors, and not
much experience with IEC applications.

Recently came across " Absorbed load " and on review became confused, perhaps you
can solve the confusion.

load factor = absorbed load / motor rating static load.

Thanks

Jeff





Go to the top of the page
 
+Quote Post
marke
post Aug 10 2008, 02:34 AM
Post #8


Posting Freak
******

Group: Moderator
Posts: 2,383
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hi Jeff

That is not a term that I use, but I expect that the "absorbed load" is the shaft power as opposed to the input power.
IEC motors are rated in maximum shaft power. Many people confuse this with the electrical input power and this is higher as it includes the motor losses.
A 10KW motor has a shaft power of 10KW and in input power at rated load of 11.5KW

Have a good day,
Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post
animna
post Aug 10 2008, 11:28 AM
Post #9


Junior Member
**

Group: Full Member
Posts: 5
Joined: 6-August 08
Member No.: 4,724



QUOTE (marke @ Aug 9 2008, 04:39 PM) *
Hello Anima

Thank you for your comments.

When you first apply full voltage to an induction motor, there is a current surge called the inrush current. This is a very short burst of current and is the current required to establish the flux in the iron.Once the iron is fluxed, the current drops down to the locked rotor current where the current is determined by the effective rotor impedance, leakage reactance and stator impedance.

When you apply power to a transformer, you also get an inrush current which is the same sort of current. - the current required to establish the flux in the iron.

Best regards,
Mark.


Dear Mr. Mark,

Thanks for your expertise.
You have respect.


Best Regards,

animna


Go to the top of the page
 
+Quote Post
bob
post Aug 10 2008, 05:09 PM
Post #10


Member
****

Group: Full Member
Posts: 187
Joined: 16-August 05
Member No.: 1,186



Dear Mark,

I understand that the LRC is a function of the characteristics of the motor. However, the inrush current is directly dependent on the mode of starting and applied voltage. Am I right ?

Best regards.

Bob


Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   2 GGOSS 5,167 28th July 2003 - 05:46 AM
Last post by: GGOSS
No New Posts   2 marke 7,765 4th July 2009 - 05:27 AM
Last post by: marke
No New Posts   0 marke 6,108 11th June 2002 - 10:34 PM
Last post by: marke
No New Posts   1 marke 4,332 7th December 2009 - 10:32 AM
Last post by: Broshi
No New Posts   0 marke 3,031 12th June 2002 - 09:24 AM
Last post by: marke