Hello and welcome to LMPForum, like most online communities you must register to view or post in our community, but don't worry this is a simple free process that requires minimal information. Take advantage of it immediately Register Now There are many great features that are not available to guests at LMPForum |
Forgot Password |
![]() ![]() |
Motor Starting, Motor Starting |
Oct 25 2009, 07:39 AM
Post
#1
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Full Member Posts: 12 Joined: 16-December 08 Member No.: 5,027 |
Hi,
I will continue a thread which I started relative to the starting of a fan. The genset , capacity 635 kVA is having trouble to meet the starting demand of the fan, capacity 90 kW. From a theoretical point of view, the Genset should have been able to start a fan of this size but for some reasons is unable to do so. I am thinking of the possibilty to reduce the voltage on the Genset so that the Genset acts as a reduced primary starter. I know that by doing so, the motor will be underfluxed but this will reduce the locked rotor current and the Genset might be able to pick up the load. The actual primary starter is of very little use. Any comment. Bob |
|
|
|
Oct 25 2009, 08:29 PM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,336 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello Bob
The primary resistance starter is not a good starter to use when starting on a genset due to the very high KW losses in the primary resistors. Reducing the voltage will reduce the locked rotor current, but so will reducing the speed. Dropping the speed down very low and then DOL, or even connecting the motor and then starting the genset could make a difference. It all depends on what other things are connected to the genset. Another thing to consider, is to look at the potential of adding a permanent magnet generator excitation system. This will provide a much higher overload current capacity for a short period of time. The combination of PMG excitation and a three phase averaging AVR system will alow a much larger motor to be connected and started by a given genset. Best regards, Mark -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Nov 1 2009, 08:27 AM
Post
#3
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Full Member Posts: 12 Joined: 16-December 08 Member No.: 5,027 |
Thanks Mark for your very fruitful advice.
Bob |
|
|
|
Nov 5 2009, 04:46 PM
Post
#4
|
|
![]() Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 668 Joined: 22-February 03 From: USA, California Member No.: 285 |
Just to reiterate something from the older thread, is this a paddle fan or a cage fan? If it's a cage type, you do have the dampers closed at start correct?
-------------------- "He's not dead, he's just pinin' for the fjords!"
|
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
2 | GGOSS | 4,682 | 28th July 2003 - 05:46 AM Last post by: GGOSS |
|||
![]() |
2 | marke | 6,843 | 4th July 2009 - 05:27 AM Last post by: marke |
|||
![]() |
0 | marke | 5,326 | 11th June 2002 - 10:34 PM Last post by: marke |
|||
![]() |
1 | marke | 3,832 | 7th December 2009 - 10:32 AM Last post by: Broshi |
|||
![]() |
0 | marke | 2,774 | 12th June 2002 - 09:24 AM Last post by: marke |
|||
|
Lo-Fi Version | Time is now: 16th March 2010 - 09:16 AM |