Motor, Imbalance
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
bob
post Sep 10 2008, 11:40 AM
Post #1


Member
****

Group: Full Member
Posts: 187
Joined: 16-August 05
Member No.: 1,186



Hi,

I have go a 90 kW immersed pump which was working trouble free before. We just started to get overload conditions on this pump. The FLC of the motor is 160 Amps. The current measured on the three phases are 165 A, 150 A and 148 A. The imbalance tends to increase with increased laod
There is no voltage imbalance. I suspect something is wrong with the motor.
Any omment.

Bob


Go to the top of the page
 
+Quote Post
marke
post Sep 10 2008, 06:41 PM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,383
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Bob

It sounds like you have a high impedance in series with one phase or one winding to do that.
Typically, submersible pumps have a high magnetising current and this makes them sensitive to any imbalance in voltage at light load, but the imbalance improves as the load increases.
To have an imbalance that gets worse as the load increases suggests that the voltage across one winding is reducing with load.
I would first try a low resistance check of the circuits that you can get at to see if you can measure any variation. It may be a joint that is going high with temperature, so I would also do a resistance check as soon as possible after the pump has been running.
I assume that you have measured the voltage while the pump is running at a high imbalance just to be sure that there is not a high impedance phase upstream of your control equipment.

Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post
bob
post Sep 22 2008, 12:36 PM
Post #3


Member
****

Group: Full Member
Posts: 187
Joined: 16-August 05
Member No.: 1,186



Hello Marke,

Thank you for your reply. We are now organising to remove and overhaul the motor. I shall keep the forum informed.

Regards.

Bob


Go to the top of the page
 
+Quote Post
bob
post Oct 4 2008, 04:10 AM
Post #4


Member
****

Group: Full Member
Posts: 187
Joined: 16-August 05
Member No.: 1,186



Hello Mark,

Bingo. We removed the motor from the well yesterday and one of the three phase cable joints in a very bad condition. The motor was supplied with only a short lead and joints had to be made. This is a case of a very bad workmanship.
Thanks again.

Bob


Go to the top of the page
 
+Quote Post
marke
post Oct 5 2008, 05:04 AM
Post #5


Posting Freak
******

Group: Moderator
Posts: 2,383
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Thanks for the update Bob,
Lets hope that is the answer!!

Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   2 GGOSS 5,160 28th July 2003 - 05:46 AM
Last post by: GGOSS
No New Posts   2 marke 7,746 4th July 2009 - 05:27 AM
Last post by: marke
No New Posts   0 marke 6,095 11th June 2002 - 10:34 PM
Last post by: marke
No New Posts   1 marke 4,324 7th December 2009 - 10:32 AM
Last post by: Broshi
No New Posts   0 marke 3,023 12th June 2002 - 09:24 AM
Last post by: marke


RSS Lo-Fi Version Time is now: 3rd September 2010 - 07:42 PM
hosted by : L M Photonics Ltd
LMPhotonics Home  Power factor  Motor Control  Single Phase Motors  Slipring Motors  Motor Starters  Soft Starters  Variable Speed  Energy Savers