Overload Relay Setting Vs Rated Current, Set OLR, how to compute if I know the rated current
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
Froilan
post Apr 6 2009, 04:02 PM
Post #1


Junior Member
**

Group: Members
Posts: 3
Joined: 6-April 09
Member No.: 5,293



How to compute for the OLR setting if the rated current is given already?
Show me the computation if the motor control starter is Across the Line, Wye Delta and Auto transformer.
Can we see a basis of this compuattion in the International electrical code?





Go to the top of the page
 
+Quote Post
Froilan
post Apr 30 2009, 01:06 PM
Post #2


Junior Member
**

Group: Members
Posts: 3
Joined: 6-April 09
Member No.: 5,293



QUOTE (Froilan @ Apr 6 2009, 08:02 AM) *
How to compute for the OLR setting if the rated current is given already?
Show me the computation if the motor control starter is Across the Line, Wye Delta and Auto transformer.
Can we see a basis of this compuattion in the International electrical code?


The OLR setting should not exceed the rated current of the motor which can be seen in the motor nameplate.
OLR Setting =< Rated Current of Motor for Across the line Motor Starter
OLR Setting = < 58% of Rated Current of Motor for Wye Delta or Auto Transformer Motor Starter
What CP 15 International Electrical Code Stated is only the OLR setting should not exceed the Rated current of motor.
Other members please help me to enlighten to enlighten up on this issue. Thanks anyway rolleyes.gif


Go to the top of the page
 
+Quote Post
marke
post Apr 30 2009, 06:52 PM
Post #3


Posting Freak
******

Group: Moderator
Posts: 2,383
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Froilan

The overload setting must not exceed the rating of the motor.
In the case of a star delta starter, the overload can be installed in series with the supply, in which case the settting must be lees than or equal to the motor rating, or it can be installed in series with the windings (most common) in which case it must be set to less than or equal to 58% of the motor ratings because the winding current is equal to 1/root(3) of the line current.
The overload setting for an auto transformer starter must not exceed the rating of the motor. (it does not measure winding current)

Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post
Froilan
post May 4 2009, 11:23 AM
Post #4


Junior Member
**

Group: Members
Posts: 3
Joined: 6-April 09
Member No.: 5,293



QUOTE (marke @ Apr 30 2009, 10:52 AM) *
Hello Froilan

The overload setting must not exceed the rating of the motor.
In the case of a star delta starter, the overload can be installed in series with the supply, in which case the settting must be lees than or equal to the motor rating, or it can be installed in series with the windings (most common) in which case it must be set to less than or equal to 58% of the motor ratings because the winding current is equal to 1/root(3) of the line current.
The overload setting for an auto transformer starter must not exceed the rating of the motor. (it does not measure winding current)

Best regards,
Mark.



The reason why I'm bringing this issue up because I just transfer my Job and it's very hard for me to implement the usual "right" practice in setting this Over Load Relay because they insist the 115% safe value of motors which I want them to be convinced that OLR setting should not exceed the rated current otherwise motor is not proteced already by this OLR or tends to shorten the life span of the Motor because of operating more than the rated capacity. What I understand on the 15% extra is the tolerance of the motor before it burn out but not to reach up to this setting. By right during the design stage the motor should be choosen 20% higher than the computed load. Please help me to have more inputs on the topic so I can correct the wrong practice in my present work. More Power! rolleyes.gif


Go to the top of the page
 
+Quote Post
marke
post May 4 2009, 06:40 PM
Post #5


Posting Freak
******

Group: Moderator
Posts: 2,383
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Froilan

There is a 15% safety margin in the ratings of the motors to allow for tolerances in the calibration of the protection devices.
Theoretically, a protection device must not trip at less than rated current and must trip at 115% rated current.
Typically, with good protection relays, the average trip point is in the order of 105% rating, but commonly there are 3% - 5% tolerances in CTs etc.
If you set the trip point at 115%, you can expect the motors to trip at 120% - 125% on average. This is enough to shorten the life of the motor.
If the protection operates late, the motor can operate at a higher temperatures and not necessarily fail immediately. Every ten degrees C hotter you run the motor, you halve it's life, so you may not see the effects of a higher overload setting for some time.

Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   3 GGOSS 2,109 22nd May 2003 - 02:34 AM
Last post by: GGOSS
No New Posts   1 -shahbaz ali- 4,881 28th August 2002 - 09:32 AM
Last post by: marke
No New Posts   0 -shahbaz ali- 2,162 --
Last post by: shahbaz ali
No New Posts   10 theDOG 2,740 25th September 2002 - 10:39 AM
Last post by: marke
No New Posts   1 tom 5,631 15th August 2003 - 04:00 PM
Last post by: merajdab


RSS Lo-Fi Version Time is now: 3rd September 2010 - 06:27 PM

Tag cloud:

hosted by : L M Photonics Ltd
LMPhotonics Home  Power factor  Motor Control  Single Phase Motors  Slipring Motors  Motor Starters  Soft Starters  Variable Speed  Energy Savers