Overload setting
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
amiruddin
post May 29 2007, 12:54 PM
Post #1



*

Group: Members
Posts: 1
Joined: 29-May 07
Member No.: 3,318



hi
i want to know how to calculate overload setting for motor AC

hi
if the AC motor have 55 KW,how we can calculate for overload setting
Go to the top of the page
 
+Quote Post
marke
post May 30 2007, 02:20 AM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,088
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello amiruddin

You set the overload relay setting to the same as the rated current of the motor.
Best regards,


--------------------
Go to the top of the page
 
+Quote Post
rene4538
post Jun 29 2007, 01:50 PM
Post #3



*

Group: Members
Posts: 1
Joined: 29-June 07
Member No.: 3,443



QUOTE(amiruddin @ May 29 2007, 12:54 PM) [snapback]6112[/snapback]

hi
i want to know how to calculate overload setting for motor AC

hi
if the AC motor have 55 KW,how we can calculate for overload setting


You can also calculate using the this formula P=I.E ,p=power ,I=current ,E=volatge then you can get the approximate motor current rating.Correct me if i am wrong.

best regards
Go to the top of the page
 
+Quote Post
marke
post Jun 29 2007, 02:14 PM
Post #4


Posting Freak
******

Group: Moderator
Posts: 2,088
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello rene4538

You have not taken into account the power factor or the efficiency which can have a major influence.

P = V x I x eff x pf

The power rating of the motor is the shaft power, not the electrical power.
The best way to determine the current rating, is to look at the motor name plate. - always shows the current rating.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post
AB2005
post Jun 30 2007, 06:21 AM
Post #5


Senior Member
*****

Group: Full Member
Posts: 216
Joined: 21-October 06
Member No.: 2,159



Normally, motors are selected 120% greater power than load. So, first, we check how much motor draws the current at the maximum working speed of machine which should be lesser than motor’s maximum current typed on the name plate. Now you can set the overload slightly at higher current under the motor full load current. This will also save your motor and your load.


--------------------
"Don't assume any thing, always check/ask and clear yourself".
Go to the top of the page
 
+Quote Post
Nitin
post Jun 30 2007, 09:19 PM
Post #6



*

Group: Members
Posts: 1
Joined: 30-June 07
Member No.: 3,450



QUOTE(amiruddin @ May 29 2007, 06:54 PM) [snapback]6112[/snapback]

hi
i want to know how to calculate overload setting for motor AC

hi
if the AC motor have 55 KW,how we can calculate for overload setting

hi
first U measure current with clampon meter and then increase relay setting 5 amp more than that.
Go to the top of the page
 
+Quote Post
chaterpilar
post Sep 5 2007, 03:34 AM
Post #7


Member
****

Group: Full Member
Posts: 165
Joined: 3-September 04
Member No.: 861



Dear Amirudin,

The more the data you will give in the question the more closer the answer will be.

For example 55 kw, at what what voltage 380 volts, 415 volts, 690 volts..?

Let us say it is a 415 volts rated motor.

In case of a star-delta starter the location of overload relay matters a lot, it can be located where 100% of current is passing through the relay or 58%is passing through.

For sake of calculation, if the motor name plate rating is 100 amps, then follow these steps.

1. Set the relay at 58 amps and start the motor and

2.Check the current at the output of relay with a clampon meter after the motor is running at its full speed and full load.

3.Let us say it is 43 amps, then set relay 3amps above 43 that is 46 amps.

A properly designed motor should have OLr setting at 80% of its full load current ( @ Name plate )

Hope it helps.

Good Luck !!


Chaterpilar

Go to the top of the page
 
+Quote Post
pelia
post Sep 13 2007, 11:17 PM
Post #8



*

Group: Members
Posts: 1
Joined: 13-September 07
Member No.: 3,779



QUOTE(amiruddin @ May 29 2007, 05:54 AM) [snapback]6112[/snapback]

hi
i want to know how to calculate overload setting for motor AC

hi
if the AC motor have 55 KW,how we can calculate for overload setting


for the overload setting
1
a) 125% of the full load current rating of a motor having a marked service factor of 1.15 or greater
cool.gif 115% of the full load current rating of the motor which does not having a marked service factor or where the service factor is less than 1.15
2
where a motor overload device is so connected that it does not carry the total current designated on the motor name plate , such as for wye-delta starting , the percentage of the motor nameplate crrent applying to the selection or setting of the overload swhall be clearly marked on the motor starter shown in the motor starter manufacturs overload selection table
Go to the top of the page
 
+Quote Post
SNSwamy
post Feb 11 2008, 05:39 PM
Post #9


Junior Member
**

Group: Members
Posts: 2
Joined: 22-April 07
Member No.: 3,191



QUOTE (amiruddin @ May 29 2007, 06:24 PM) *
hi
i want to know how to calculate overload setting for motor AC

hi
if the AC motor have 55 KW,how we can calculate for overload setting



find the actual running of the motor Check the voltage.depending on the load set the relay to that load if it is less than full load & if the load is more than full load set the relay at full load of motor
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
2 User(s) are reading this topic (2 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   6 gogo 1,050 11th January 2003 - 08:55 PM
Last post by: TheOne
No New Posts   1 Les L 1,188 8th December 2004 - 08:04 AM
Last post by: -Anonymous-
No New Posts   13 GGOSS 3,626 20th November 2003 - 02:21 AM
Last post by: jraef
No New Posts   1 merajdab 972 16th August 2003 - 10:19 PM
Last post by: marke
No New Posts   1 normannicklette 1,806 1st November 2004 - 08:01 AM
Last post by: RalphChristie



RSS Lo-Fi Version Time is now: 16th October 2008 - 12:05 AM
hosted by : L M Photonics Ltd