IPB


Welcome Guest ( Log In | Register )

 
Reply to this topicStart new topic
PFC Installation Savings
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
Guest__*
post Dec 7 2005, 01:38 PM
Post #1





Guests






We are considering installing pfc equipment in our factory.

We are on a 11,000 volt ring main along with 2 other neighbouring companies. (Several years ago our factory was part of a large group occupying this site, our neighbours were once part of this group but have now been sold off). We have our own transformer, LV switches and distribution system. We are billed for our power from a neighbouring company - they read the meter monthly 'downstream' of our transformer and charge us accordingly.

We are advised that if we install pfc we will only see a small proportion of the savings. The capacitors would be installed on the LV side of the power network, but could someone explain why we won't achieve all of the savings?

Thanks in advance!
Go to the top of the page
 
+Quote Post
marke
post Dec 7 2005, 05:54 PM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,099
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hi

If you are paying for KW only, you wil get little or no savings.
Power factor correction does not alter the KW drawn by the motor. It will reduce the reactive current drawn from the supply and this will only affect you KWHrs if you have significant line losses between the metering and where the correction is connected. If you are paying a PF penalty, or a KVA demand charge, then you wil achieve a saving, otherwise I would not expect a worthwhile payback.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   4 jraef 1,661 26th October 2004 - 09:37 AM
Last post by: -Anonymous-
No New Posts   5 klangwcng 1,787 18th December 2005 - 09:51 AM
Last post by: marke
No New Posts   0 -Raymond- 995 6th February 2006 - 12:39 PM
Last post by: Raymond
No New Posts   0 Murph095 1,009 4th April 2006 - 12:55 PM
Last post by: Murph095
No New Posts 4 FLOW_EE 1,164 25th August 2006 - 06:53 PM
Last post by: FLOW_EE



RSS Lo-Fi Version Time is now: 21st November 2008 - 08:21 PM
hosted by : L M Photonics Ltd