Parallel operation of Gens
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
chaterpilar
post Nov 2 2005, 11:48 AM
Post #1


Member
****

Group: Full Member
Posts: 165
Joined: 3-September 04
Member No.: 861



We intend to buy 10nos. 1600kva Cat gens (60Hz) for a Load of 12 MVA and are looking at 3 options...

a) make all 10 in sync and feed the common to Distribution board or...

b) make 2 sets of 5 Gens each (in sync) and feed it to Distribution board, with a bus coupler

c) Is it possible to furthur synchronise the two banks of 5 gens and then close the buscoupler.

Please give your views about advantages and disadvantages of each option.

Thanks

Chaterpilar


Go to the top of the page
 
+Quote Post
Guest__*
post Nov 2 2005, 02:29 PM
Post #2





Guests






Suggest you contact the Experts ie

FG Wilson - Larne - N. Ireland.
mailto:sales (at) fgwilson (dot) com


Go to the top of the page
 
+Quote Post
chaterpilar
post Nov 5 2005, 10:02 AM
Post #3


Member
****

Group: Full Member
Posts: 165
Joined: 3-September 04
Member No.: 861



Marke,


I am waiting for your valuable opinion.


regards,

Chaterpilar


Go to the top of the page
 
+Quote Post
GGOSS
post Nov 6 2005, 10:37 PM
Post #4


Senior Member
*****

Group: Moderator
Posts: 404
Joined: 17-May 02
From: Melbourne
Member No.: 14



Hello Chaterpilar,

Just a quick note to let you know Marke is travelling overseas this week and may not have ready access to the internet.

Unfortunately I do not have enough gen-set experience to provide you with any sound advice. Hopefully some of the other forum members will be able to assist you further.

Regards,
GGOSS


Go to the top of the page
 
+Quote Post
Guest__*
post Nov 8 2005, 07:53 PM
Post #5





Guests






Hello Chaterpilar,

What you are proposing to do is not at all difficult, and I have commissioned a few multiple parrallel diesel generator sets. If you want to organise all the gerneators on to a single bus that is fine, or if you want them on two buses that is also fine. Automatic synchronising, load control and scheduling on/off of the generators as the load changes is also easily done.

16MVA at 400V is going to require some very big bus bars, you may have to run a single bus as you might not be able to get a bus tie breaker that can handle the fault current, or are you going to have MV generators at 3.3kV or higher?

Is the generation going to supply the load in isolation or will it run in parrallel with a utility network?

Regards
Niallnz


Go to the top of the page
 
+Quote Post
chaterpilar
post Nov 10 2005, 09:03 AM
Post #6


Member
****

Group: Full Member
Posts: 165
Joined: 3-September 04
Member No.: 861



hello,

Thanks for your reply.

well the generators will be synchronised and then 400v outputs will be sent to 400/13.8kv step up X-mer

Each gen will have 1 step up X-mer.

The 13.8kv sync bus will have utility supply with castle interlocks

I wanted toknow which arrangement will be easier and good for reliability 10 gens in sync or 2 banks of 5 gen in sync and then the two banks in sync.

regards

chaterpilar


Go to the top of the page
 
+Quote Post
niallnz
post Nov 16 2005, 09:37 PM
Post #7


Intermediate Member
***

Group: Full Member
Posts: 27
Joined: 5-November 02
From: Christchurch
Member No.: 165



Hello Chaterpilar,

Just to confirm, each generator will be directly connected to their own step up transformer, therefore the synchronising will take place across the 13.8kV CB. The 13.8kV bus will also have 1 only connection to the utility.

In this case I would connect all 10 gens onto the one bus. Why are you interlocking the utility supply? I would set up the generator controllers to also control the utility breaker, and control the generator output for zero power import/export across the utility CB if that is what is required. The generator controllers will be able to synchronise the gen bus to the utility upon the return of the utility supply after a failure. Alternatively the control can be bumpless transfer between the utility supply and the generator supply, ie which enough generators are on line to take the local load the utlity CB will be opened.

I think that 10 gens one to the one bus will be easier to set up and more reliable.

BR
Niallnz


Go to the top of the page
 
+Quote Post
chaterpilar
post Nov 21 2005, 02:46 PM
Post #8


Member
****

Group: Full Member
Posts: 165
Joined: 3-September 04
Member No.: 861



Hello Niall,

The synchronisation will take place at 400 volts ( LV side of the step up transformer).

We are in favour of 10 gens in sync.. but the issuethere is if the Sync panel develops a fault ...then all gens are down..

If you do 5 in sync..and then the other 5 in sync then atleast 5 gens are in operation even if 1 sync panel is down.

Actually syncing..10 gens is easier...but reliability of Sync panel becomes a risky factor.

We are not going synchronise gen supply with utility supply..they are just mechanicalyy interlocked ( Castell lock)

regards,

narayan


Go to the top of the page
 
+Quote Post
niallnz
post Nov 24 2005, 11:28 PM
Post #9


Intermediate Member
***

Group: Full Member
Posts: 27
Joined: 5-November 02
From: Christchurch
Member No.: 165



Hello Narayan,

Typically in power stations the synchroniser is in a trolley that is wheeled to each generator control panel. And a synch trolley can be a simple as three lights, so the chances of it developing a fault that can't be fixed in a hurry are very low. So I take it that this power station will be manually operated?.

Personnally I would be controlling these gensets with a Woodward EGCP-3 on each unit. The EGCP-3 is a synchroniser and load controller so no sync panel required. The EGCP's communicate between each other and can start/stop the generators to match the load. The EGCP can also automatically balance out the running hours on the gens amongst other things.

I would also do a true unit connection of the generator and the transformer and sync across the HV CB, but remember to install and a CB in the generator field circuit which can be tripped by the generator/transformer protection. It may not seem like much but you save yourself the cost of the LV switchgear, terminations, panel etc and when a generator is off line your not wasting energy keeping a transformer warm. There are no transformer inrush issues as when you excite the generator you also excite the transformer and this done from 0volts.

I'd be happy to design supply and commission a generator control system for you. ;)

Cheers Niall


Go to the top of the page
 
+Quote Post
Seema K
post Sep 9 2008, 06:17 AM
Post #10



*

Group: Members
Posts: 1
Joined: 9-September 08
Member No.: 4,800



Hello Niall

First of all apologies for intervening.

Cuntinuing the conversation, have you considered the impact of shortcircuit level of the common busbar? NGR?

Regards,
S

QUOTE (niallnz @ Nov 25 2005, 04:28 AM) *
Hello Narayan,

Typically in power stations the synchroniser is in a trolley that is wheeled to each generator control panel. And a synch trolley can be a simple as three lights, so the chances of it developing a fault that can't be fixed in a hurry are very low. So I take it that this power station will be manually operated?.

Personnally I would be controlling these gensets with a Woodward EGCP-3 on each unit. The EGCP-3 is a synchroniser and load controller so no sync panel required. The EGCP's communicate between each other and can start/stop the generators to match the load. The EGCP can also automatically balance out the running hours on the gens amongst other things.

I would also do a true unit connection of the generator and the transformer and sync across the HV CB, but remember to install and a CB in the generator field circuit which can be tripped by the generator/transformer protection. It may not seem like much but you save yourself the cost of the LV switchgear, terminations, panel etc and when a generator is off line your not wasting energy keeping a transformer warm. There are no transformer inrush issues as when you excite the generator you also excite the transformer and this done from 0volts.

I'd be happy to design supply and commission a generator control system for you. wink.gif

Cheers Niall


Go to the top of the page
 
+Quote Post
martin
post Sep 19 2008, 03:59 AM
Post #11


Intermediate Member
***

Group: Full Member
Posts: 15
Joined: 23-August 07
From: Singapore
Member No.: 3,670



Hi There,
Have read the post with interest!
I would say buy the best system that has the best local service support for you're area/region in the world. Whilst Woodward EGCP-3 has been mentioned as a solution, which I'm not saying is correct, is your local rep/service people able to handle this?
Had huge problem setting-up in Indonesia rig a system on this brand and found the support.....wanting!!!!
I personally use a Heinzmann, out of Germany....again lot of software,......I guess I'm saying for such a complicated system speak to the suppliers in your region and ask for references of their stuff actually working.
Regards
Martin


Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   4 GGOSS 2,369 14th December 2008 - 06:08 PM
Last post by: marke
No New Posts   2 -Anonymous- 991 21st October 2004 - 06:00 PM
Last post by: marke
No New Posts   3 mazona 1,361 23rd May 2005 - 07:00 PM
Last post by: marke
No new   21 bob 1,838 13th September 2005 - 04:34 AM
Last post by: bob
No New Posts   5 hadi 1,349 7th September 2005 - 05:34 AM
Last post by: bob


RSS Lo-Fi Version Time is now: 15th March 2010 - 10:37 PM

Tag cloud:

hosted by : L M Photonics Ltd
LMPhotonics Home  Power factor  Motor Control  Single Phase Motors  Slipring Motors  Motor Starters  Soft Starters  Variable Speed  Energy Savers