Hello and welcome to LMPForum, like most online communities you must register to view or post in our community, but don't worry this is a simple free process that requires minimal information. Take advantage of it immediately Register Now There are many great features that are not available to guests at LMPForum |
Forgot Password |
![]() ![]() |
Power Factor Correction |
Jun 21 2009, 02:00 AM
Post
#1
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Full Member Posts: 37 Joined: 28-September 08 From: Kuala Lumpur Member No.: 4,848 |
Hi,
How can we add capacitor bank to a new installation which has inductive loads such as motor and fluorescent lights without knowing the total power factor? Kana |
|
|
|
Jun 21 2009, 06:43 AM
Post
#2
|
|
|
Member ![]() ![]() ![]() ![]() Group: Full Member Posts: 77 Joined: 13-June 09 Member No.: 5,502 |
Inductive load is not constant - it is changing all the time as motors (major "culprits" of disbalance) switch on and off, as their loads change, as other - "active" - consumers of energy switch on and off (and proportion of working active and inductive loads thus changing). So if you chose a steady capacitance there may be moments when it would not be correcting the power factor, but instead, itself introduce reactive currents.
Probably you would not do without a special automatic appliance which monitors the disbalance and regulates capacitance needed. |
|
|
|
Jun 21 2009, 07:06 AM
Post
#3
|
|
|
Member ![]() ![]() ![]() ![]() Group: Full Member Posts: 77 Joined: 13-June 09 Member No.: 5,502 |
However, if you are tight on budget, find some minimal load at that place which indeed remains constant throughout the working day. Then, I see it so : measuring the apparent currant add - safely, through switches - capacitors, so, that the curr was dropping. Add so much cap-s untill curr stops decreasing. The resultant capacitance will be equal to the reactive inductance at that particular, constant, load.
All the best, I hope having not said an utter nonsense. I meant doing it on the major feeder at that place - applying appropriate cap-s and with all the safety measures. |
|
|
|
Jun 21 2009, 12:57 PM
Post
#4
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Full Member Posts: 37 Joined: 28-September 08 From: Kuala Lumpur Member No.: 4,848 |
Hi,
Yes, I understand that but what I meant was how do we estimate the size of capacitor bank(bulk correction) during the designing stage of a new electrical system, say for a high rise building or an industrial plant? Are we supposed to take in account the power factor of each load which will be connected to the system? Is there any other method? Kana |
|
|
|
Jun 21 2009, 05:27 PM
Post
#5
|
|
|
Member ![]() ![]() ![]() ![]() Group: Full Member Posts: 77 Joined: 13-June 09 Member No.: 5,502 |
El motors have power factor on their name plates. I believe other equipment must have that too in their specifiactions. It seems fluorescent fixtures already contain a cap for the PF correction. I am not an expert on that issue, but probably, one calculates all the reactive loads and choses capacitance.
|
|
|
|
Jul 2 2009, 03:28 AM
Post
#6
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Full Member Posts: 37 Joined: 28-September 08 From: Kuala Lumpur Member No.: 4,848 |
Yes, that's right motors have their power factor stated at their name plate. As for lights, we assume that all lights have pf correction capacitor installed. From what I heard, during the designing stage of an electrical installation we assume the overall power factor to be 0.8 and we do a power factor correction so the overall power factor would be 0.95. I’m not sure about this but I really appreciate if anyone could clarify this.
Regards, Kana |
|
|
|
Jul 4 2009, 05:32 AM
Post
#7
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,336 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello kana
You do need to have some idea of what the reactive current is before you can neutralise it. If you have motors on the supply, it is normal for the name plate to indicate the full load power factor. From this information, you can calculate the reactive current for each motor. You can then add all the reactive curents and apply correction for this current. The best method is to measure the reactive current or the power factor. Best regards, Mark. -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Jul 4 2009, 11:58 AM
Post
#8
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Full Member Posts: 37 Joined: 28-September 08 From: Kuala Lumpur Member No.: 4,848 |
Thanks Mark & Yuri.
Regards, Kana |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
1 | -Billy- | 5,584 | 6th May 2002 - 10:22 PM Last post by: marke |
|||
![]() |
0 | Asad | 3,822 | 11th May 2002 - 03:24 AM Last post by: Asad |
|||
![]() |
62 | marke | 26,302 | 27th December 2008 - 03:58 AM Last post by: marke |
|||
![]() |
2 | Itos | 4,091 | 13th August 2002 - 03:40 PM Last post by: nadeem1990pk |
|||
![]() |
4 | Itos | 4,828 | 24th June 2002 - 04:02 AM Last post by: Itos |
|||
|
Lo-Fi Version | Time is now: 11th March 2010 - 10:59 AM |