Power Factor Correction, Supply
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
bob14
post Oct 21 2009, 07:11 AM
Post #1


Intermediate Member
***

Group: Full Member
Posts: 15
Joined: 16-December 08
Member No.: 5,027



Hi Mark,

I have been reading the fantastic papers you wrote on bulk and static corrections. It is a known fact that by implementing power factor corrections, consumers would hardly benefit on k Wh consumption but rather on power factor penalties instead.
However, in the case of power generation, improving power factor would also mean that the kW generated by a plant would remain the same though the kVA demand on the generator would decrease. This obviously mean that the current drawn from the generator would be less for the same kW consumption. Does it mean that the generating plant would save on fuel consumption ? I doubt as the prime mover is always rated in k W .

Best regards .

Bob


Go to the top of the page
 
+Quote Post
marke
post Oct 21 2009, 08:16 AM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,383
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hi Bob

The engine is loaded by KW and the KW of the load will not change with the addition of power factor correction, however the KVA will reduce with power factor correction and this in turn will reduce the I2r losses in the alternator, reducing the KW drawn from the engine.
The reduction in KVA will also reduce the KW losses in the cables between the alternator and the correction.

Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post
bob14
post Oct 21 2009, 09:25 AM
Post #3


Intermediate Member
***

Group: Full Member
Posts: 15
Joined: 16-December 08
Member No.: 5,027



Dear Mark,

Thanks for your prompt reply. This therefore means that the saving in fuel would only be marginal.

Regards;

Bob


Go to the top of the page
 
+Quote Post
marke
post Oct 21 2009, 06:01 PM
Post #4


Posting Freak
******

Group: Moderator
Posts: 2,383
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Bob

Yes, however a saving is still a saving.
The savings will depend on the efficiency of the alternator.

If you have a power factor of 0.5 and an alternator efficiency of 50%, then the savings would be significant. If your power factor is more like 0.9 and the alternator efficiency is say 95%, then the savings will be small.

If you have a low power factor, improving the poser factor will enable you to run with more connected load on the genset which can mean shutting one genset down in situations where there are multiple gensets operating together.

Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   3 -Billy- 6,346 14th June 2010 - 05:22 PM
Last post by: jOmega
No New Posts   0 Asad 4,268 11th May 2002 - 03:24 AM
Last post by: Asad
No new   65 marke 28,252 12th August 2010 - 01:24 PM
Last post by: TTC
No New Posts   2 Itos 4,512 13th August 2002 - 03:40 PM
Last post by: nadeem1990pk
No New Posts   4 Itos 5,847 24th June 2002 - 04:02 AM
Last post by: Itos


RSS Lo-Fi Version Time is now: 3rd September 2010 - 05:08 PM
hosted by : L M Photonics Ltd
LMPhotonics Home  Power factor  Motor Control  Single Phase Motors  Slipring Motors  Motor Starters  Soft Starters  Variable Speed  Energy Savers