Hello and welcome to LMPForum, like most online communities you must register to view or post in our community, but don't worry this is a simple free process that requires minimal information. Take advantage of it immediately Register Now There are many great features that are not available to guests at LMPForum |
Forgot Password |
![]() ![]() |
Power Factor Correction, Supply |
Oct 21 2009, 07:11 AM
Post
#1
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Full Member Posts: 15 Joined: 16-December 08 Member No.: 5,027 |
Hi Mark,
I have been reading the fantastic papers you wrote on bulk and static corrections. It is a known fact that by implementing power factor corrections, consumers would hardly benefit on k Wh consumption but rather on power factor penalties instead. However, in the case of power generation, improving power factor would also mean that the kW generated by a plant would remain the same though the kVA demand on the generator would decrease. This obviously mean that the current drawn from the generator would be less for the same kW consumption. Does it mean that the generating plant would save on fuel consumption ? I doubt as the prime mover is always rated in k W . Best regards . Bob |
|
|
|
Oct 21 2009, 08:16 AM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,383 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hi Bob
The engine is loaded by KW and the KW of the load will not change with the addition of power factor correction, however the KVA will reduce with power factor correction and this in turn will reduce the I2r losses in the alternator, reducing the KW drawn from the engine. The reduction in KVA will also reduce the KW losses in the cables between the alternator and the correction. Best regards, Mark. -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Oct 21 2009, 09:25 AM
Post
#3
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Full Member Posts: 15 Joined: 16-December 08 Member No.: 5,027 |
Dear Mark,
Thanks for your prompt reply. This therefore means that the saving in fuel would only be marginal. Regards; Bob |
|
|
|
Oct 21 2009, 06:01 PM
Post
#4
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,383 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello Bob
Yes, however a saving is still a saving. The savings will depend on the efficiency of the alternator. If you have a power factor of 0.5 and an alternator efficiency of 50%, then the savings would be significant. If your power factor is more like 0.9 and the alternator efficiency is say 95%, then the savings will be small. If you have a low power factor, improving the poser factor will enable you to run with more connected load on the genset which can mean shutting one genset down in situations where there are multiple gensets operating together. Best regards, Mark. -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
3 | -Billy- | 6,346 | 14th June 2010 - 05:22 PM Last post by: jOmega |
|||
![]() |
0 | Asad | 4,268 | 11th May 2002 - 03:24 AM Last post by: Asad |
|||
![]() |
65 | marke | 28,252 | 12th August 2010 - 01:24 PM Last post by: TTC |
|||
![]() |
2 | Itos | 4,512 | 13th August 2002 - 03:40 PM Last post by: nadeem1990pk |
|||
![]() |
4 | Itos | 5,847 | 24th June 2002 - 04:02 AM Last post by: Itos |
|||
|
Lo-Fi Version | Time is now: 3rd September 2010 - 05:08 PM |