Can Power Be Saved By Running Motor In Star Mode At No Load?
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
barani
post Dec 23 2006, 05:25 PM
Post #1


Junior Member
**

Group: Members
Posts: 4
Joined: 23-December 06
Member No.: 2,716



in STARDELTA starters the mode(from star to delta) automatically changes after a specified time period..
MY QUESTION IS..
*when a motor is running in no load and if we use some controllers to make the (star delta)starter to stay in Star mode itself, can power be saved, as we are applying only 1/root(3) of the line voltage to the motor
*we can sense the load current and change it to delta once the motor gets loaded..
*because in industries the motor might not carry load at all the times.. so on no load we can switch it back to star and save the power ..
*pl tell me whether my concept will work. if this is correct i will choose this as my project..
Go to the top of the page
 
+Quote Post
marke
post Dec 23 2006, 07:06 PM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,118
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello barani

Yes, you will reduce the iron losses when the motor is connected in star, but the transition from star to delta is normally an open tranistion and causes a major current and torque transient which can do damage to the driven load and create electrical interference.
You would be best to use a closed transition and there are additional losses in doing so.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post
jraef
post Dec 23 2006, 10:28 PM
Post #3


Posting Freak
******

Group: Moderator
Posts: 658
Joined: 22-February 03
From: USA, California
Member No.: 285



Plus your mechanical load on the motor in Star would need to be 1/3 or less of the full load capacity in Delta, otherwise you will overload the motor in Star and no energy will be saved. Unless of course you count the fact that the motor has tripped off line as an energy savings!


--------------------
"He's not dead, he's just pinin' for the fjords!"
Go to the top of the page
 
+Quote Post
barani
post Dec 24 2006, 01:54 AM
Post #4


Junior Member
**

Group: Members
Posts: 4
Joined: 23-December 06
Member No.: 2,716



hello jraef,
thank u very much for answering . i have a doubt.... u told "mechanical load on the motor in Star would need to be 1/3 or less of the full load capacity in Delta, otherwise you will overload the motor in Star and no energy will be saved. " how can we fix the cut off point as 1/3 of full load? pl give me derivations if any. it will be helpful for me.
Go to the top of the page
 
+Quote Post
barani
post Dec 24 2006, 05:12 PM
Post #5


Junior Member
**

Group: Members
Posts: 4
Joined: 23-December 06
Member No.: 2,716



Dear marke,
thank you very much for spending time for answering me.
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   1 -Billy- 3,362 6th May 2002 - 10:22 PM
Last post by: marke
No New Posts   0 Asad 2,363 11th May 2002 - 03:24 AM
Last post by: Asad
No new   62 marke 19,370 27th December 2008 - 03:58 AM
Last post by: marke
No New Posts   2 GGOSS 3,113 28th July 2003 - 05:46 AM
Last post by: GGOSS
No New Posts   0 marke 3,628 11th June 2002 - 10:32 PM
Last post by: marke



RSS Lo-Fi Version Time is now: 8th January 2009 - 07:20 PM
hosted by : L M Photonics Ltd