Can Power Be Saved By Running Motor In Star Mode At No Load? |
![]() ![]() |
Can Power Be Saved By Running Motor In Star Mode At No Load? |
Dec 23 2006, 05:25 PM
Post
#1
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 4 Joined: 23-December 06 Member No.: 2,716 |
in STARDELTA starters the mode(from star to delta) automatically changes after a specified time period..
MY QUESTION IS.. *when a motor is running in no load and if we use some controllers to make the (star delta)starter to stay in Star mode itself, can power be saved, as we are applying only 1/root(3) of the line voltage to the motor *we can sense the load current and change it to delta once the motor gets loaded.. *because in industries the motor might not carry load at all the times.. so on no load we can switch it back to star and save the power .. *pl tell me whether my concept will work. if this is correct i will choose this as my project.. |
|
|
|
Dec 23 2006, 07:06 PM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,118 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello barani
Yes, you will reduce the iron losses when the motor is connected in star, but the transition from star to delta is normally an open tranistion and causes a major current and torque transient which can do damage to the driven load and create electrical interference. You would be best to use a closed transition and there are additional losses in doing so. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Dec 23 2006, 10:28 PM
Post
#3
|
|
![]() Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 658 Joined: 22-February 03 From: USA, California Member No.: 285 |
Plus your mechanical load on the motor in Star would need to be 1/3 or less of the full load capacity in Delta, otherwise you will overload the motor in Star and no energy will be saved. Unless of course you count the fact that the motor has tripped off line as an energy savings!
-------------------- "He's not dead, he's just pinin' for the fjords!"
|
|
|
|
Dec 24 2006, 01:54 AM
Post
#4
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 4 Joined: 23-December 06 Member No.: 2,716 |
hello jraef,
thank u very much for answering . i have a doubt.... u told "mechanical load on the motor in Star would need to be 1/3 or less of the full load capacity in Delta, otherwise you will overload the motor in Star and no energy will be saved. " how can we fix the cut off point as 1/3 of full load? pl give me derivations if any. it will be helpful for me. |
|
|
|
Dec 24 2006, 05:12 PM
Post
#5
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 4 Joined: 23-December 06 Member No.: 2,716 |
Dear marke,
thank you very much for spending time for answering me. |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
1 | -Billy- | 3,362 | 6th May 2002 - 10:22 PM Last post by: marke |
|||
![]() |
0 | Asad | 2,363 | 11th May 2002 - 03:24 AM Last post by: Asad |
|||
![]() |
62 | marke | 19,370 | 27th December 2008 - 03:58 AM Last post by: marke |
|||
![]() |
2 | GGOSS | 3,113 | 28th July 2003 - 05:46 AM Last post by: GGOSS |
|||
![]() |
0 | marke | 3,628 | 11th June 2002 - 10:32 PM Last post by: marke |
|||
|
Lo-Fi Version | Time is now: 8th January 2009 - 07:20 PM |