Hello and welcome to LMPForum, like most online communities you must register to view or post in our community, but don't worry this is a simple free process that requires minimal information. Take advantage of it immediately Register Now There are many great features that are not available to guests at LMPForum |
Forgot Password |
![]() ![]() |
Reacceleration Protection |
Sep 6 2007, 05:03 AM
Post
#1
|
|
|
Junior Member ![]() ![]() Group: Full Member Posts: 7 Joined: 5-September 07 Member No.: 3,743 |
What is Reacceleration protection in Induction motor?
Please clarify this. |
|
|
|
Sep 6 2007, 07:41 PM
Post
#2
|
|
![]() Senior Member ![]() ![]() ![]() ![]() ![]() Group: Full Member Posts: 213 Joined: 15-March 05 From: Milan, Italy Member No.: 1,068 |
VSP,
one possible reply is: big motors cannot be started too frequently, specially if load inertia is high. For some minutes after starting, during deceleration for loss of power, this protection will avoid that the motor will restart, reaching an hot temperature in the rotor. Other explainations are possible. Regards Mario -------------------- |
|
|
|
Sep 7 2007, 05:11 AM
Post
#3
|
|
![]() Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 668 Joined: 22-February 03 From: USA, California Member No.: 285 |
Another version is to protect against short term power losses that may allow a motor to be reconnected to the line before the magnetic field collapses. If that happens, the motor may still be in regeneration and when reconnected, the two power sources are out of sync, which causes a violent voltage spike. Re-acceleration protection just ensures that on 2-wire control systems, if the power goes out, however briefly, there will always be a delay of a few seconds before the motor controller reconnects to the line.
-------------------- "He's not dead, he's just pinin' for the fjords!"
|
|
|
|
Sep 7 2007, 06:40 AM
Post
#4
|
|
|
Junior Member ![]() ![]() Group: Full Member Posts: 7 Joined: 5-September 07 Member No.: 3,743 |
QUOTE(jraef @ Sep 7 2007, 10:41 AM) [snapback]6714[/snapback] Another version is to protect against short term power losses that may allow a motor to be reconnected to the line before the magnetic field collapses. If that happens, the motor may still be in regeneration and when reconnected, the two power sources are out of sync, which causes a violent voltage spike. Re-acceleration protection just ensures that on 2-wire control systems, if the power goes out, however briefly, there will always be a delay of a few seconds before the motor controller reconnects to the line. Is that mean Re-accleration protection stop motor has voltage spike(supply voltage drop below undervoltage) occurs and Start motor after specifid delay? |
|
|
|
Nov 29 2008, 08:40 AM
Post
#5
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 4 Joined: 27-November 08 Member No.: 4,988 |
|
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
0 | marke | 5,326 | 11th June 2002 - 10:34 PM Last post by: marke |
|||
![]() |
1 | -mahesh- | 2,163 | 4th April 2006 - 06:08 AM Last post by: khongai |
|||
![]() |
3 | tahira | 3,806 | 22nd August 2003 - 09:01 AM Last post by: sethar |
|||
![]() |
0 | tahira | 967 | -- Last post by: tahira |
|||
![]() |
1 | normannicklette | 2,490 | 1st November 2004 - 08:01 AM Last post by: RalphChristie |
|||
|
Lo-Fi Version | Time is now: 16th March 2010 - 09:14 AM |