Hello and welcome to LMPForum, like most online communities you must register to view or post in our community, but don't worry this is a simple free process that requires minimal information. Take advantage of it immediately Register Now There are many great features that are not available to guests at LMPForum |
Forgot Password |
![]() ![]() |
Siemens Soft Start |
Dec 16 2008, 06:02 PM
Post
#1
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 2 Joined: 16-December 08 Member No.: 5,029 |
Need help with Siemens 3RW3024-1AB14 soft start. After installation, we pushed start button and 480 volt motor will not work. We measured 280v from each phase to ground, but we are not getting 480v phase to phase. Incoming voltage is correct. Control voltage is 120v and motor is 5hp serving an overhead crane. This soft start is replacing a Benshaw LTS controller that has gone bad. Any help would be greatly appreciated.
Thanks, |
|
|
|
Dec 17 2008, 07:17 AM
Post
#2
|
|
![]() Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 668 Joined: 22-February 03 From: USA, California Member No.: 285 |
Need help with Siemens 3RW3024-1AB14 soft start. After installation, we pushed start button and 480 volt motor will not work. We measured 280v from each phase to ground, but we are not getting 480v phase to phase. Incoming voltage is correct. Control voltage is 120v and motor is 5hp serving an overhead crane. This soft start is replacing a Benshaw LTS controller that has gone bad. Any help would be greatly appreciated. Thanks, Describe what you mean by "close the start button". What is the start button wired to? On the 3RW30, you need to first close any upstream contactor, then you must also power control board and close the control circuit between control terminals A1 and IN1. You must also have the other half of your control circuit connected to control terminal A2. So for example if you are using 120V control, you would wire the hot of the 120V control power to A1, a Start / Run command between A1 and IN1, and the neutral to A2. -------------------- "He's not dead, he's just pinin' for the fjords!"
|
|
|
|
Dec 17 2008, 01:13 PM
Post
#3
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 2 Joined: 16-December 08 Member No.: 5,029 |
Describe what you mean by "close the start button". What is the start button wired to? On the 3RW30, you need to first close any upstream contactor, then you must also power control board and close the control circuit between control terminals A1 and IN1. You must also have the other half of your control circuit connected to control terminal A2. So for example if you are using 120V control, you would wire the hot of the 120V control power to A1, a Start / Run command between A1 and IN1, and the neutral to A2. Thanks for your input. We didn't have control wiring connected properly and have corrected the problem. Works fine now. |
|
|
|
Dec 19 2008, 11:42 PM
Post
#4
|
|
![]() Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 668 Joined: 22-February 03 From: USA, California Member No.: 285 |
Thanks for your input. We didn't have control wiring connected properly and have corrected the problem. Works fine now. Glad to here it. -------------------- "He's not dead, he's just pinin' for the fjords!"
|
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
34 | marke | 18,673 | 10th July 2009 - 04:11 AM Last post by: wrav001 |
|||
![]() |
5 | uhaykir | 4,431 | 5th July 2002 - 09:08 AM Last post by: marke |
|||
![]() |
1 | marke | 3,243 | 14th July 2003 - 12:44 AM Last post by: GGOSS |
|||
![]() |
3 | -Ravisankar- | 3,074 | 28th June 2002 - 08:04 AM Last post by: GGOSS |
|||
![]() |
8 | GGOSS | 2,404 | 18th August 2003 - 07:00 AM Last post by: GGOSS |
|||
|
Lo-Fi Version | Time is now: 16th March 2010 - 09:13 AM |