Hello and welcome to LMPForum, like most online communities you must register to view or post in our community, but don't worry this is a simple free process that requires minimal information. Take advantage of it immediately Register Now There are many great features that are not available to guests at LMPForum |
Forgot Password |
![]() ![]() |
Slipring Motor Power Consumption, Slipring motor power consumption |
Sep 10 2009, 08:59 AM
Post
#1
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 2 Joined: 8-September 09 Member No.: 6,455 |
Dear All,
I am using slipring motor of 425KW, 6.6 KV. motor for fan application. Motor speed is controlled using grid resistance and it is running at 80% speed. As I know for fan applications power = (speed) 3. Does this formula applies to slip ring motor also? or it applies to VFD + Induction motor. As i know if slip ring motor running at 80% speed, remaining slip power dissipates at resistors and there will no energy saving. Finally my intension is to use VFD+S.C. motor instead of slipring motor. |
|
|
|
Sep 10 2009, 07:02 PM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,383 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello santhosh80
Welcome to the forum Yes, the power required by the fan is proportional to the speed cubed. When you slow the fan down using any method, the torque required will reduce. When you use a slip ring motor to slow the fan down, the torque reduces and the speed of the motor reduces increasing the slip. Because the torque has reduced, the power drawn from the supply will reduce, but the power dissipated in the rotor resistors increases. The rotor power is still part of the total power into the motor which is reducing with torque, so the power consumed by the fan is much less than at full speed and the power drawn from the supply is reduced by a lesser amount. At 80 percent speed, 80 percent of the power consumed (less than full power) is drawn by the load and the remaining 20% is dissipated in the rotor resistors. Using the slip ring motor to reduce the speed will result in energy savings, but eliminating the slip losses will yield higher savings. Short the rings and us a VFD and you will eliminate the slip losses. Best regards, Mark. -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Sep 12 2009, 02:09 PM
Post
#3
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 2 Joined: 8-September 09 Member No.: 6,455 |
Thanks a lot! Marke. I agree as per your reply, that power consumption of the motor reduces when we reduce speed of the fan irrespective of type of motor. But if we see the main draw back of the slipring motors is low p.f at low speeds when compared to induction motor + VFD. As the power factor reduces in slipring motors when we reduce the speed, does this has no effect in the input power consumption of the motor at lower speeds? Regards, Santhosh. |
|
|
|
Sep 12 2009, 08:13 PM
Post
#4
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,383 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello Santosh
I do not expect the power factor to drop as the motor is slowed down by adding rotor resistance. I would expect that the power factor would be high. The problem is that the magnetic field is rotating at synchronous speed and the rotor is spinning at less than synchronous speed. Therefore, there are high slip losses. If we take a motor running at half speed, half the power in to the motor is driving the load and the other half is heating the rotor resistors due to slip losses. The efficiency of the motor and rotor resistors reduces as the rotor resistance is increased. Best regards, Mark -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
3 | -Billy- | 6,346 | 14th June 2010 - 05:22 PM Last post by: jOmega |
|||
![]() |
0 | Asad | 4,269 | 11th May 2002 - 03:24 AM Last post by: Asad |
|||
![]() |
65 | marke | 28,256 | 12th August 2010 - 01:24 PM Last post by: TTC |
|||
![]() |
2 | GGOSS | 5,160 | 28th July 2003 - 05:46 AM Last post by: GGOSS |
|||
![]() |
2 | marke | 7,746 | 4th July 2009 - 05:27 AM Last post by: marke |
|||
|
Lo-Fi Version | Time is now: 3rd September 2010 - 08:01 PM |