I used omron MY2N control relays to drive the DC24V current to turn on/off the hydraulic valves. I found that the spark will occur between the contact during turned off the control relay. Is there any countermeasure for me to dissipate the spark? Thanks
|
|
|
|
Mar 13 2008, 04:47 AM
Post
#2
|
|
![]() Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 658 Joined: 22-February 03 From: USA, California Member No.: 285 |
-------------------- "He's not dead, he's just pinin' for the fjords!"
|
|
|
|
Mar 13 2008, 06:25 AM
Post
#3
|
|
|
Junior Member ![]() ![]() Group: Full Member Posts: 6 Joined: 26-November 06 Member No.: 2,416 |
Thanks you very much. Anyway, now my connection is +24V-->Contact-->Valve-->0V. Is that i need to change to +24V-->Valve-->Contact-->0V before add in the additional diod between the 2 terminal of hydraulic valve? Is there any other way to do it? And, how about for AC 220V?
|
|
|
|
Mar 13 2008, 06:31 AM
Post
#4
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,118 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello Jacky
There are a number of options that can be used. One option, is to connect a diode across the coil so that it is reverse polarised when the voltage is applied to the coil. This will stop the arc, but will dramatically slow down the reduction in current flow through the coil. This can make the valve operation sluggish. To speed up the release of the field in the coil, you can connect a resistor in series with the diode. This will allow the field to collapse at a greater rate, but will also increase the back emf generated by the coil. Another method is to connect an MOV across the relay contacts. This will limit the voltage across the contacts and reduce the arcing. A snubber network across the contacts will have a similar effect, but wil be less effective. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
14 | GGOSS | 2,763 | 2nd January 2008 - 07:14 AM Last post by: jraef |
|||
![]() |
2 | GGOSS | 3,113 | 28th July 2003 - 05:46 AM Last post by: GGOSS |
|||
![]() |
3 | rup_loc | 1,422 | 30th May 2005 - 07:32 PM Last post by: Carl |
|||
![]() |
17 | BigMax | 2,164 | 14th October 2002 - 08:04 AM Last post by: theDOG |
|||
![]() |
8 | -ed- | 1,382 | 15th March 2005 - 12:29 PM Last post by: -Anonymous- |
|||
|
Lo-Fi Version | Time is now: 8th January 2009 - 07:41 PM |