I used omron MY2N control relays to drive the DC24V current to turn on/off the hydraulic valves. I found that the spark will occur between the contact during turned off the control relay. Is there any countermeasure for me to dissipate the spark? Thanks
Go to the top of the page
 
+Quote Post
jraef
post Mar 13 2008, 04:47 AM
Post #2


Posting Freak
******

Group: Moderator
Posts: 658
Joined: 22-February 03
From: USA, California
Member No.: 285



Yes, it's called "inductive kickback".

http://www.coilgun.info/theory/inductivekickback.htm


--------------------
"He's not dead, he's just pinin' for the fjords!"
Go to the top of the page
 
+Quote Post
Jacky
post Mar 13 2008, 06:25 AM
Post #3


Junior Member
**

Group: Full Member
Posts: 6
Joined: 26-November 06
Member No.: 2,416



Thanks you very much. Anyway, now my connection is +24V-->Contact-->Valve-->0V. Is that i need to change to +24V-->Valve-->Contact-->0V before add in the additional diod between the 2 terminal of hydraulic valve? Is there any other way to do it? And, how about for AC 220V?
Go to the top of the page
 
+Quote Post
marke
post Mar 13 2008, 06:31 AM
Post #4


Posting Freak
******

Group: Moderator
Posts: 2,118
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Jacky

There are a number of options that can be used.
One option, is to connect a diode across the coil so that it is reverse polarised when the voltage is applied to the coil.
This will stop the arc, but will dramatically slow down the reduction in current flow through the coil. This can make the valve operation sluggish.
To speed up the release of the field in the coil, you can connect a resistor in series with the diode. This will allow the field to collapse at a greater rate, but will also increase the back emf generated by the coil.

Another method is to connect an MOV across the relay contacts. This will limit the voltage across the contacts and reduce the arcing.

A snubber network across the contacts will have a similar effect, but wil be less effective.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No new   14 GGOSS 2,763 2nd January 2008 - 07:14 AM
Last post by: jraef
No New Posts   2 GGOSS 3,113 28th July 2003 - 05:46 AM
Last post by: GGOSS
No New Posts   3 rup_loc 1,422 30th May 2005 - 07:32 PM
Last post by: Carl
No new   17 BigMax 2,164 14th October 2002 - 08:04 AM
Last post by: theDOG
No New Posts   8 -ed- 1,382 15th March 2005 - 12:29 PM
Last post by: -Anonymous-



RSS Lo-Fi Version Time is now: 8th January 2009 - 07:41 PM
hosted by : L M Photonics Ltd