How i can calculate starting current for the water booster pumps 220 kw
|
|
|
|
Mar 28 2008, 01:36 PM
Post
#2
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 3 Joined: 15-March 08 Member No.: 4,391 |
|
|
|
|
Apr 3 2008, 08:28 AM
Post
#3
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,063 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello JONY
In order to calculate the starting current of the pumps, you need to know a number of parameters. Firstly, the minimum start current is determined by the minimum start torque of the pumps and the ability of the motor to develop that torque, plus the start method employed. If you start the motors on Full Voltage, they will always draw Locked Rotor Current, Independent of connected load, and will have a starting current typically in the range of 600% - 900% of the rated current of the motor. If you use a reduced voltage starter, the current will be reduced by the voltage reduction and the torque will be reduced by the voltage reduction squared. If you reduce the start voltage too much, you will not produce sufficient torque to start the pump. By drawing out the speed torque curve of the pump, and overlaying the speed torque curve of the motor at different start settings, you can determine the minimum starting current of the pump and motor. NB each motor has different starting characteristics, so the calculations need to be done for each motor. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Jun 13 2008, 07:06 AM
Post
#4
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 2 Joined: 11-June 08 Member No.: 4,616 |
Hello JONY In order to calculate the starting current of the pumps, you need to know a number of parameters. Firstly, the minimum start current is determined by the minimum start torque of the pumps and the ability of the motor to develop that torque, plus the start method employed. If you start the motors on Full Voltage, they will always draw Locked Rotor Current, Independent of connected load, and will have a starting current typically in the range of 600% - 900% of the rated current of the motor. If you use a reduced voltage starter, the current will be reduced by the voltage reduction and the torque will be reduced by the voltage reduction squared. If you reduce the start voltage too much, you will not produce sufficient torque to start the pump. By drawing out the speed torque curve of the pump, and overlaying the speed torque curve of the motor at different start settings, you can determine the minimum starting current of the pump and motor. NB each motor has different starting characteristics, so the calculations need to be done for each motor. Best regards, very good |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
1 | -ksvs29- | 1,442 | 15th August 2002 - 09:22 PM Last post by: marke |
|||
![]() |
1 | andromeda | 1,379 | 14th November 2002 - 10:02 PM Last post by: marke |
|||
![]() |
1 | -shahbaz ali- | 1,846 | 28th August 2002 - 09:32 AM Last post by: marke |
|||
![]() |
0 | -shahbaz ali- | 1,185 | -- Last post by: shahbaz ali |
|||
![]() |
10 | theDOG | 1,589 | 25th September 2002 - 10:39 AM Last post by: marke |
|||
|
Lo-Fi Version | Time is now: 7th September 2008 - 04:44 PM |