Starting Current
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
Subramanian
post Aug 14 2009, 06:09 AM
Post #1


Junior Member
**

Group: Members
Posts: 2
Joined: 14-August 09
Member No.: 6,201



We would like to have a 600KW 415V centrifugal air Comressor.As this has to run on Gas Generator supply,what is the type of starter that can be used.
We would like to have a min Starting current.As centrifugal Compressor has to operate on fixed speed, speed variation is not required.
We would like to know who can supplysuitable starter.What will be the min Starting current possible.

Thanks
AGS


Go to the top of the page
 
+Quote Post
marke
post Aug 14 2009, 07:58 AM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,336
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Subramanian

Welcome to the forum.

The minimum start current is a function of the minimum load torque required (determined by the compressor) and the motor design.
The first step is to obtain the compressor speed torque curve during start to determine the required start torque.
The second step is to obtain the motor curves for torque against speed and current against speed at full voltage.

As you reduce the start voltage, the current reduces by the same ratio and the torque reduces by the square of the current reduction.
With this knowledge, you can plot a series of start torque curves for different start voltages or different start currents and can then determine the lowest current that can start the compressor.
A good soft starter is an economic way of regulating the start current.
If you need to further reduce the start current, you can consider the motor selection and look for a rotor design that has more resistance and produces a higher torque at a lower start current. (There are big differences between motor designs.)
Alternatively, look at a wound rotor motor and a slip ring starter, or a VFD.

Have a look at http://www.lmphotonics.com/m_control.htm and http://www.lmphotonics.com/m_start.htm

Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post
Subramanian
post Aug 17 2009, 10:56 AM
Post #3


Junior Member
**

Group: Members
Posts: 2
Joined: 14-August 09
Member No.: 6,201



QUOTE (marke @ Aug 14 2009, 08:58 AM) *
Hello Subramanian

Welcome to the forum.

The minimum start current is a function of the minimum load torque required (determined by the compressor) and the motor design.
The first step is to obtain the compressor speed torque curve during start to determine the required start torque.
The second step is to obtain the motor curves for torque against speed and current against speed at full voltage.

As you reduce the start voltage, the current reduces by the same ratio and the torque reduces by the square of the current reduction.
With this knowledge, you can plot a series of start torque curves for different start voltages or different start currents and can then determine the lowest current that can start the compressor.
A good soft starter is an economic way of regulating the start current.
If you need to further reduce the start current, you can consider the motor selection and look for a rotor design that has more resistance and produces a higher torque at a lower start current. (There are big differences between motor designs.)
Alternatively, look at a wound rotor motor and a slip ring starter, or a VFD.

Have a look at http://www.lmphotonics.com/m_control.htm and http://www.lmphotonics.com/m_start.htm

Best regards,
Mark.





Hello Mr.Mark

Thanks for your prompt guidance.



Best Regards

Subramanian





Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   1 -ksvs29- 2,653 15th August 2002 - 09:22 PM
Last post by: marke
No New Posts   1 andromeda 2,065 14th November 2002 - 10:02 PM
Last post by: marke
No New Posts   1 -shahbaz ali- 4,092 28th August 2002 - 09:32 AM
Last post by: marke
No New Posts   0 -shahbaz ali- 1,943 --
Last post by: shahbaz ali
No New Posts   10 theDOG 2,548 25th September 2002 - 10:39 AM
Last post by: marke


RSS Lo-Fi Version Time is now: 13th March 2010 - 09:35 PM

Tag cloud:

hosted by : L M Photonics Ltd
LMPhotonics Home  Power factor  Motor Control  Single Phase Motors  Slipring Motors  Motor Starters  Soft Starters  Variable Speed  Energy Savers