Submersible Well Pump Chews Contactors
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
Mark Monson
post Feb 16 2009, 09:59 PM
Post #1


Junior Member
**

Group: Full Member
Posts: 7
Joined: 23-August 07
Member No.: 3,679



I have a wee technical problem that I would appreciate some wisdom on :

A customer of my employer installed a submersible well pump on a farm. The pump is a Davey brand 1.12HP submersible The installation is a fairly typical rural irrigation-pump with a centrifugal pump about 70m down the well. The pump draws a balanced 2.6A per phase in normal running. Starting is DOL, using one of our 4KW DOL starters and an appropriately-rated Thermal Overload relay. Being a centrifugal pump, I am told that the starting load is quite light.

The problem is that the line contactor keeps getting its contacts chewed. Given that it is good for about 4x as much motor power as it is switching, this should not be happening. When the first contactor fried, it could be dismissed as one rogue contactor, but when a second fried too, there is clearly something wrong, but what?

The float switches are sufficiently far apart that frequent on/off cycling can be ruled out. The thermal overload is set to manual reset, so it is not cycling on/off due to the TOR tripping. There is no PFC installed, and there are no co-connected loads. Like most NZ electrical contractors, this one has a Megger and knows how to use it, and all seems well as far as insulation resistance goes.

Thoughts, anyone?


Go to the top of the page
 
+Quote Post
marke
post Feb 17 2009, 09:36 AM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,383
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hi Mark

The two most common reasons for this that I come across, are :
  1. Chattering contacts due to control circuit. Fluttering level switches and the like. Arrange the circuit so that the contactor is latched closed. A single pulse from the top float closes the contactor and it is held closed by an early close contact. If the pulses from the float are very quick, it can be possible for the contactor to partially close and then open several times before sealing closed. Using a relay to interface and provide the latch function will be faster and may eliminate the bounce.
  2. Low coil voltage. If there is a voltage drop during start, the voltage on the coil of the contactor will be reduced. If the voltage drops more than 15%, it is possible for the magnetic poles to begin to separate and the pressure on the contacts to reduce.
    If the contact pressure is reduced during start, the contact resistance will increase and the contact temperature will rise causing premature failure.
I would suggest that you use a high speed logger to monitor the voltage across the coil during start and this will probably show you the cause of the problem.

Best regards,
Mark.


--------------------


Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No new   17 BigMax 3,049 14th October 2002 - 08:04 AM
Last post by: theDOG
No New Posts   2 Shink 6,117 8th October 2003 - 01:41 AM
Last post by: grobert
No New Posts   3 -mgendron- 1,557 8th October 2003 - 01:56 AM
Last post by: grobert
No New Posts   1 Kirk 1,242 12th September 2003 - 07:36 AM
Last post by: marke
No New Posts   0 -Anonymous- 968 9th November 2004 - 06:17 PM
Last post by: -Anonymous-


RSS Lo-Fi Version Time is now: 7th September 2010 - 03:55 PM

Tag cloud:

hosted by : L M Photonics Ltd
LMPhotonics Home  Power factor  Motor Control  Single Phase Motors  Slipring Motors  Motor Starters  Soft Starters  Variable Speed  Energy Savers