Supply Distortion by drive
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
marke
post May 13 2002, 09:37 AM
Post #1


Posting Freak
******

Group: Moderator
Posts: 2,383
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



I am involved in an existing installation with a large pump that shares a supply transformer with two consumers houses. The inverter is a significant load and well exceeds the combined loads of the houses. The transformer is fed by a long overhead 11KV line.

When the pump is running, one house has problems with the harmonics generated by the VFD but the other does not. Both houses are fed directly from the transformer terminals with underground cables.
The inverter is fitted with DC Bus chokes and also with a coupled three phase inductor on the input.
The inverter is rated at about 70% of the transformer rating.
One solution to the problem is to install a second transformer to supply the two houses but that is an expensive option. Is there a cheaper and effective option that is guaranteed to work??


--------------------


Go to the top of the page
 
+Quote Post
Tractor
post Jan 6 2010, 04:27 PM
Post #2



*

Group: Members
Posts: 1
Joined: 6-January 10
Member No.: 7,496



QUOTE (marke @ May 13 2002, 09:37 AM) *
I am involved in an existing installation with a large pump that shares a supply transformer with two consumers houses. The inverter is a significant load and well exceeds the combined loads of the houses. The transformer is fed by a long overhead 11KV line.

When the pump is running, one house has problems with the harmonics generated by the VFD but the other does not. Both houses are fed directly from the transformer terminals with underground cables.
The inverter is fitted with DC Bus chokes and also with a coupled three phase inductor on the input.
The inverter is rated at about 70% of the transformer rating.
One solution to the problem is to install a second transformer to supply the two houses but that is an expensive option. Is there a cheaper and effective option that is guaranteed to work??


Go to the top of the page
 
+Quote Post
Davemell0
post Feb 13 2010, 08:55 PM
Post #3


Junior Member
**

Group: Full Member
Posts: 7
Joined: 16-July 09
Member No.: 5,871



QUOTE (marke @ May 13 2002, 10:37 AM) *
I am involved in an existing installation with a large pump that shares a supply transformer with two consumers houses. The inverter is a significant load and well exceeds the combined loads of the houses. The transformer is fed by a long overhead 11KV line.

When the pump is running, one house has problems with the harmonics generated by the VFD but the other does not. Both houses are fed directly from the transformer terminals with underground cables.
The inverter is fitted with DC Bus chokes and also with a coupled three phase inductor on the input.
The inverter is rated at about 70% of the transformer rating.
One solution to the problem is to install a second transformer to supply the two houses but that is an expensive option. Is there a cheaper and effective option that is guaranteed to work??


Marke

If you talk to someone like MTE corporation they may be able to help you guys out. A six pulse drive can be quite noisy even with a DC bus choke and input reactor. So I think your two options are to install a new transformer, or to install a harmonic filter. The harmonic filter should work fine, but I do not know how its cost will compare to the transformer. This is not meant as a promotion of MTE, they are just an example of a potential source for harmonic filters. Also since you have dc bus chokes and an input reactor I am assuming this is a low voltage drive, if it is a medium voltage drive you will have to purchase a custom harmonic filter for your exact application.

Thanks


Dave


Go to the top of the page
 
+Quote Post
PowerQualityDoct...
post Feb 14 2010, 06:32 PM
Post #4


Junior Member
**

Group: Members
Posts: 3
Joined: 14-February 10
Member No.: 7,790



What are the affects on the house? You cannot "kill" all the harmonics (even with active filters), but can reduce their affect.

You can also try to change the switching frequency. It can change the amount of distortion, but more important can change the results as sometimes specific frequency creates a resonance.



--------------------
Free Power Quality analysis at http://www.powerqualitydoctor.com


Go to the top of the page
 
+Quote Post
jOmega
post Mar 11 2010, 05:17 AM
Post #5


Member
****

Group: Full Member
Posts: 179
Joined: 26-February 06
From: Midwest, USA
Member No.: 1,401



QUOTE (PowerQualityDoctor @ Feb 14 2010, 12:32 PM) *
What are the affects on the house? You cannot "kill" all the harmonics (even with active filters), but can reduce their affect.

You can also try to change the switching frequency. It can change the amount of distortion, but more important can change the results as sometimes specific frequency creates a resonance.




Au Contraire. Neither assertion is correct.



--------------------


Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   13 marke 6,975 13th July 2010 - 10:31 AM
Last post by: elmger
No New Posts   0 weiwei2 4,740 1st October 2002 - 02:37 PM
Last post by: weiwei2
No new   32 kongkc 7,306 13th November 2005 - 07:09 PM
Last post by: -Anonymous-
No New Posts   4 GGOSS 2,697 14th December 2008 - 06:08 PM
Last post by: marke
No New Posts   4 incal 1,690 17th January 2003 - 08:51 PM
Last post by: incal


RSS Lo-Fi Version Time is now: 3rd September 2010 - 04:53 PM
hosted by : L M Photonics Ltd
LMPhotonics Home  Power factor  Motor Control  Single Phase Motors  Slipring Motors  Motor Starters  Soft Starters  Variable Speed  Energy Savers