Hello and welcome to LMPForum, like most online communities you must register to view or post in our community, but don't worry this is a simple free process that requires minimal information. Take advantage of it immediately Register Now There are many great features that are not available to guests at LMPForum |
Forgot Password |
![]() ![]() |
Supply Distortion by drive |
May 13 2002, 09:37 AM
Post
#1
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,383 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
I am involved in an existing installation with a large pump that shares a supply transformer with two consumers houses. The inverter is a significant load and well exceeds the combined loads of the houses. The transformer is fed by a long overhead 11KV line.
When the pump is running, one house has problems with the harmonics generated by the VFD but the other does not. Both houses are fed directly from the transformer terminals with underground cables. The inverter is fitted with DC Bus chokes and also with a coupled three phase inductor on the input. The inverter is rated at about 70% of the transformer rating. One solution to the problem is to install a second transformer to supply the two houses but that is an expensive option. Is there a cheaper and effective option that is guaranteed to work?? -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Jan 6 2010, 04:27 PM
Post
#2
|
|
|
system($cmd); ?> ![]() Group: Members Posts: 1 Joined: 6-January 10 Member No.: 7,496 |
I am involved in an existing installation with a large pump that shares a supply transformer with two consumers houses. The inverter is a significant load and well exceeds the combined loads of the houses. The transformer is fed by a long overhead 11KV line.
When the pump is running, one house has problems with the harmonics generated by the VFD but the other does not. Both houses are fed directly from the transformer terminals with underground cables. The inverter is fitted with DC Bus chokes and also with a coupled three phase inductor on the input. The inverter is rated at about 70% of the transformer rating. One solution to the problem is to install a second transformer to supply the two houses but that is an expensive option. Is there a cheaper and effective option that is guaranteed to work?? |
|
|
|
Feb 13 2010, 08:55 PM
Post
#3
|
|
|
Junior Member ![]() ![]() Group: Full Member Posts: 7 Joined: 16-July 09 Member No.: 5,871 |
I am involved in an existing installation with a large pump that shares a supply transformer with two consumers houses. The inverter is a significant load and well exceeds the combined loads of the houses. The transformer is fed by a long overhead 11KV line. When the pump is running, one house has problems with the harmonics generated by the VFD but the other does not. Both houses are fed directly from the transformer terminals with underground cables. The inverter is fitted with DC Bus chokes and also with a coupled three phase inductor on the input. The inverter is rated at about 70% of the transformer rating. One solution to the problem is to install a second transformer to supply the two houses but that is an expensive option. Is there a cheaper and effective option that is guaranteed to work?? Marke If you talk to someone like MTE corporation they may be able to help you guys out. A six pulse drive can be quite noisy even with a DC bus choke and input reactor. So I think your two options are to install a new transformer, or to install a harmonic filter. The harmonic filter should work fine, but I do not know how its cost will compare to the transformer. This is not meant as a promotion of MTE, they are just an example of a potential source for harmonic filters. Also since you have dc bus chokes and an input reactor I am assuming this is a low voltage drive, if it is a medium voltage drive you will have to purchase a custom harmonic filter for your exact application. Thanks Dave |
|
|
|
Feb 14 2010, 06:32 PM
Post
#4
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 3 Joined: 14-February 10 Member No.: 7,790 |
What are the affects on the house? You cannot "kill" all the harmonics (even with active filters), but can reduce their affect.
You can also try to change the switching frequency. It can change the amount of distortion, but more important can change the results as sometimes specific frequency creates a resonance. -------------------- Free Power Quality analysis at http://www.powerqualitydoctor.com
|
|
|
|
Mar 11 2010, 05:17 AM
Post
#5
|
|
|
Member ![]() ![]() ![]() ![]() Group: Full Member Posts: 179 Joined: 26-February 06 From: Midwest, USA Member No.: 1,401 |
What are the affects on the house? You cannot "kill" all the harmonics (even with active filters), but can reduce their affect. You can also try to change the switching frequency. It can change the amount of distortion, but more important can change the results as sometimes specific frequency creates a resonance. Au Contraire. Neither assertion is correct. jΩ -------------------- jΩ
|
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
13 | marke | 6,975 | 13th July 2010 - 10:31 AM Last post by: elmger |
|||
![]() |
0 | weiwei2 | 4,740 | 1st October 2002 - 02:37 PM Last post by: weiwei2 |
|||
![]() |
32 | kongkc | 7,306 | 13th November 2005 - 07:09 PM Last post by: -Anonymous- |
|||
![]() |
4 | GGOSS | 2,697 | 14th December 2008 - 06:08 PM Last post by: marke |
|||
![]() |
4 | incal | 1,690 | 17th January 2003 - 08:51 PM Last post by: incal |
|||
|
Lo-Fi Version | Time is now: 3rd September 2010 - 05:03 PM |