Dec 4 2003, 05:14 PM
Post
#1
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 5 Joined: 29-October 03 Member No.: 537 |
Can I use a capacitor with passive filter to improve the pf of the motorwith a VSD?;p;
|
|
|
|
Dec 4 2003, 06:35 PM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,115 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello Daniel
1. You must never connect any form of capacitor on the output of a VSD or soft starter without the manufacturers approval. 2. The power factor seen by the supply when using a VSD with a motor, is that of the VSD, the power factor of the motor is irrelevant due to the DC link. 3. The power factor of a VSD varies, but is less than 1 due to the presence of harmonics, rather than inductive current. To improve the power factor of a VSD, you need to use a filter in series with the input. This can range from a simple line reactor to a comples filter assembly, depending on the specifications required. - talk to the VSD manufacturer. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
1 | Itos | 1,670 | 26th June 2002 - 08:56 PM Last post by: marke |
|||
![]() |
1 | marke | 2,226 | 2nd November 2006 - 03:23 AM Last post by: AB2005 |
|||
![]() |
1 | rup_loc | 1,172 | 20th July 2002 - 05:43 AM Last post by: marke |
|||
![]() |
1 | Lewis | 1,681 | 28th September 2002 - 01:37 AM Last post by: marke |
|||
![]() |
3 | Lewis | 1,615 | 8th October 2002 - 05:53 PM Last post by: marke |
|||
|
Lo-Fi Version | Time is now: 7th January 2009 - 10:23 PM |