Hello and welcome to LMPForum, like most online communities you must register to view or post in our community, but don't worry this is a simple free process that requires minimal information. Take advantage of it immediately Register Now There are many great features that are not available to guests at LMPForum |
Forgot Password |
![]() ![]() |
Use Of Vfd In Centrifugal Compressor |
Feb 20 2009, 06:18 PM
Post
#1
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 3 Joined: 20-February 09 From: Ahmedabad-India Member No.: 5,168 |
Dear All,
Hello, i am looking for any references for putting VFD for centrifugal compressors. Has any one done this application with any VFD? My customer wants to maintain the starting current around 100 to 110 %. Can we drop the frequency with auto loop with Pressure transmitter giving control to the VFD? The rating is 410 KW / 600 KW and 650 KW motors, at 2970 rpm and 415 VAC supply / 50 hz. Thanking you, awaiting your reply at the earliest. Best regards, Abhay Upadhye MIFA SYSTEMS Ahmedabad India |
|
|
|
Feb 24 2009, 06:54 AM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,336 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello Abhay
Welcome to the forum This is done very commonly these days as a means of increasing the operating efficiency of screw compressors and the like. Rather than off load the compressors and keep them operating at full speed, the speed is reduced and operates on demand in the same way that a pump control system operates. The reduction in speed reduces the losses in the system. The reduction in start current is another advantage in many installations. Best regards, Mark. -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Feb 24 2009, 07:11 AM
Post
#3
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 3 Joined: 20-February 09 From: Ahmedabad-India Member No.: 5,168 |
Hello Abhay Welcome to the forum This is done very commonly these days as a means of increasing the operating efficiency of screw compressors and the like. Rather than off load the compressors and keep them operating at full speed, the speed is reduced and operates on demand in the same way that a pump control system operates. The reduction in speed reduces the losses in the system. The reduction in start current is another advantage in many installations. Best regards, Mark. Dear Mark, Thanks for your reply and welcoming me to the forum, well i appreciate your reply and inputs, we are system integrator for Yaskawa for last 15 years and have done lots of applications including compressors, but all the time we have given drives on reciprocating or scroll compressors. we had a real lengthy discussion with the designers of Centrifugal compressor manufacturers and all of them are opposing that the speed of this type of compressor can not be dropped?!! We are very confident that dropping the speed between certain band will not cause any harm, but those people are reluctant on the subject, thus i wanted to know that if anyone has done a specific speed reduction job on Centrifugal compressors with any make VFD; so once we have any reference on the subject we can take up the issue with the supplier, our end user is very keen to do so, but he will also have to have permission from the supplier of the compressor or there could be warranttee issues which he would not like to jeopardise. Thanking you and waiting for your reply. With best regards, Abhay Upadhye MIFA SYSTEMS www.mifasystems.com |
|
|
|
Mar 2 2009, 01:29 PM
Post
#4
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 3 Joined: 20-February 09 From: Ahmedabad-India Member No.: 5,168 |
Hello all,
Any news on the said subject? it seem no one has used VFD on centrifugal compressor!!! Regards, Abhay Dear Mark,
Thanks for your reply and welcoming me to the forum, well i appreciate your reply and inputs, we are system integrator for Yaskawa for last 15 years and have done lots of applications including compressors, but all the time we have given drives on reciprocating or scroll compressors. we had a real lengthy discussion with the designers of Centrifugal compressor manufacturers and all of them are opposing that the speed of this type of compressor can not be dropped?!! We are very confident that dropping the speed between certain band will not cause any harm, but those people are reluctant on the subject, thus i wanted to know that if anyone has done a specific speed reduction job on Centrifugal compressors with any make VFD; so once we have any reference on the subject we can take up the issue with the supplier, our end user is very keen to do so, but he will also have to have permission from the supplier of the compressor or there could be warranttee issues which he would not like to jeopardise. Thanking you and waiting for your reply. With best regards, Abhay Upadhye MIFA SYSTEMS www.mifasystems.com |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
3 | bbeer | 1,525 | 29th November 2004 - 03:44 AM Last post by: -Anonymous- |
|||
![]() |
1 | bingobong62 | 1,069 | 5th November 2003 - 06:41 PM Last post by: marke |
|||
![]() |
3 | autopaint | 982 | 31st July 2005 - 11:24 PM Last post by: GGOSS |
|||
![]() |
5 | RCinFL | 4,530 | 20th September 2005 - 01:18 AM Last post by: RCinFL |
|||
![]() |
3 | sanjoy_datta49 | 1,445 | 28th September 2005 - 02:26 PM Last post by: -Anonymous- |
|||
|
Lo-Fi Version | Time is now: 14th March 2010 - 07:15 AM |