Hello and welcome to LMPForum, like most online communities you must register to view or post in our community, but don't worry this is a simple free process that requires minimal information. Take advantage of it immediately Register Now There are many great features that are not available to guests at LMPForum |
Forgot Password |
![]() ![]() |
Vsd At A High Distance |
Feb 5 2009, 05:45 PM
Post
#1
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 4 Joined: 27-April 08 Member No.: 4,525 |
i have VSD 400 m away from motor. it is not possible to relocate either of them.
what option do I have , to suppress harmonics and meet EMC regulations ? do I have limitation for using shielded cable for control cable from motor to VSD? We have asked for external filter but from the catalogues , I am not sure that this distance is workable. can someone guide me? |
|
|
|
Feb 11 2009, 05:45 PM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,336 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello shatabdi
Yes, there are limits to the maximum length of cable that can be connected to the output of a VFD and a shorter length for screened cable. These limits are the maximum that the VFD can be connected to and still be reliable. These cable lengths vary considerably between different VFDs and different manufacturers so this information needs to come from the manufacturer. In addition, there are limits to the lengths of the cable that can be connected and the installation still operate with in the EMC requirements or CE. In general, it is necessary to use a screened cable in order to comply with the EMC emissions regulations, and with some VFDs, it is possible to use up to 150M of screened cable and still comply, but with other designs, the maximum cable length can be as short as 5 meters. Your supplier should be able to tell you what the limits are for you VFD. Some suppliers can provide additional filters that you connect to the output of the VFD to extend the maximum cable length and comply. You need to talk to your supplier to get a definite answer. Best regards, Mark. -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Feb 15 2009, 08:27 AM
Post
#3
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 4 Joined: 27-April 08 Member No.: 4,525 |
Hello shatabdi Yes, there are limits to the maximum length of cable that can be connected to the output of a VFD and a shorter length for screened cable. These limits are the maximum that the VFD can be connected to and still be reliable. These cable lengths vary considerably between different VFDs and different manufacturers so this information needs to come from the manufacturer. In addition, there are limits to the lengths of the cable that can be connected and the installation still operate with in the EMC requirements or CE. In general, it is necessary to use a screened cable in order to comply with the EMC emissions regulations, and with some VFDs, it is possible to use up to 150M of screened cable and still comply, but with other designs, the maximum cable length can be as short as 5 meters. Your supplier should be able to tell you what the limits are for you VFD. Some suppliers can provide additional filters that you connect to the output of the VFD to extend the maximum cable length and comply. You need to talk to your supplier to get a definite answer. Best regards, Mark. Thank you Mark . for me the length is 400 m , and supplier insists 400 m is not possible for him . I hve asked for filter . any site where I can check what filter to be selected for certain distance ? Regards |
|
|
|
Feb 15 2009, 05:42 PM
Post
#4
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,336 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
The difficulty that you have, is if you require EMC compatibility, then you must comply with the manufacturers instructions. Adding a filter may allow operation over 400M with out damage to the VFD, but unless you pay a lot for testing, will not comply with EMC requirments in terms of providing proof of operation.
Additionally, unless you have the manufacturers recommendations as to the filter to use, you will not know if the filter will provide sufficient protection for the VFD for reliable operation. If the supplier is not able to give recommendations, you need to change supplier. Best regards, Mark. -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Jul 5 2009, 10:44 AM
Post
#5
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 3 Joined: 5-July 09 From: China Member No.: 5,755 |
I think the distance seems a bit long. There is alway limitation for length between the motor and VSD.
Maybe you can contact the manufacturer for more. -------------------- |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
0 | GGOSS | 1,143 | 29th November 2002 - 05:26 AM Last post by: GGOSS |
|||
![]() |
4 | noble | 1,971 | 2nd November 2004 - 07:55 AM Last post by: RalphChristie |
|||
![]() |
3 | Otto | 2,032 | 2nd February 2004 - 07:30 AM Last post by: jraef |
|||
![]() |
4 | boomer | 1,366 | 3rd August 2004 - 08:38 PM Last post by: jraef |
|||
![]() |
2 | chaterpilar | 1,023 | 4th September 2004 - 11:46 AM Last post by: chaterpilar |
|||
|
Lo-Fi Version | Time is now: 14th March 2010 - 03:35 PM |