Hello and welcome to LMPForum, like most online communities you must register to view or post in our community, but don't worry this is a simple free process that requires minimal information. Take advantage of it immediately Register Now There are many great features that are not available to guests at LMPForum |
Forgot Password |
![]() ![]() |
Vsd, Installation |
Nov 29 2009, 10:38 AM
Post
#1
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Full Member Posts: 12 Joined: 16-December 08 Member No.: 5,027 |
Hi,
We are planning to install a dozen of VSDs, 7.5 kW 400 V, on a new site. The panel powering the VSDs are loaded with a power factor correction capacity bank. The bank is permanently powered. Having been through the forum, I am wondering how the local capacity bank could affect the performance of the VSDs. The VSDs are of the Siemens micomaster type. Thanks. Bob |
|
|
|
Nov 29 2009, 05:45 PM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,336 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hi Bob
When you say that the capacitors are permanently powered, I assume by that you mean that they are not switched at all. This is most unusual!! The action of the capacitors will be to amplify transients which could be enough under some conditions to damage the inputs to the VFDs, and also to increase the transient fault current so that the VFDs, when hit by a line transient, are more likely to be damaged due to the current magnitude. I would recommend fitting AC line reactors if the capacitors are closer than 50M in cable length from the VFDs. Best regards, Mark. -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Nov 30 2009, 04:09 AM
Post
#3
|
|
|
Senior Member ![]() ![]() ![]() ![]() ![]() Group: Full Member Posts: 277 Joined: 21-October 06 Member No.: 2,159 |
I would recommend fitting AC line reactors if the capacitors are closer than 50M in cable length from the VFDs. Best regards, Mark. Hello Mark, Great info. But if capacitors are switched through PF controller then?? It too need to install line reactor under such installation? -------------------- "Don't assume any thing, always check/ask and clear yourself".
|
|
|
|
Nov 30 2009, 08:16 AM
Post
#4
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,336 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello AB2005
Yes, the act of switching the capacitors creates transients and the low impedance causes the transient currents to be high enough to cause problems. Best regards, Mark. -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
![]() ![]() |
|